Results 1 to 7 of 7
  1. #1
    Join Date
    Dec 2006
    Location
    new england
    Posts
    751
    Post Likes

    Trane Intellipack question

    I have 3 I-packs in a bldg. that I just recently took over. A 20,30 and 40 ton. m/n sxhfc.... Installed in 98". I'm getting faults of o/a sensor fail and evap temp sense fail. Where are these sensors located in the unit. I'm reading the manuals as we speak and can't find anything. Tia Fitz

  2. #2
    Join Date
    Jan 2010
    Location
    Central Texas
    Posts
    206
    Post Likes
    O/A should be at the opposite corner of the unit from the Control Panel. That is if you are looking at the Control Panel, it would be to the left on the backside of the unit.

    Evap Temp Sensor is in the Blower section, just after the Coil.

    That is if my memory serves me right.

  3. #3
    Join Date
    Dec 2006
    Location
    new england
    Posts
    751
    Post Likes
    Thread Starter
    Thanks for the help. Fitz

  4. #4
    Join Date
    Aug 2010
    Location
    Middle GA
    Posts
    104
    Post Likes
    OA sensor is behind the mist eliminators / louvers at the back of the rtu in the outside air intake section. Evap sensor should be mounted to the suction line in the location sgraefe said.

  5. #5
    Join Date
    Mar 2007
    Posts
    3,629
    Post Likes
    Since these are older units, the evap temp sensor is located on the suction line in a well. The new 410a Intellipaks have an additional sensor on the distributor tubing for saturated evaporator temperature.
    The key to happiness is lower expectations.

    Don't pick the fly crap out of the pepper.

  6. #6
    Join Date
    Jun 2006
    Location
    midwest
    Posts
    135
    Post Likes

    oas

    oas is ;located in the return air section behind the power exhaust term. boards and the evap sensor is located in the supply fan section on the suction line

  7. #7
    Join Date
    Dec 2006
    Location
    new england
    Posts
    751
    Post Likes
    Thread Starter
    Thanks guys.