Results 1 to 7 of 7
    Dec 2006
    new england
    Trane Intellipack question
    I have 3 I-packs in a bldg. that I just recently took over. A 20,30 and 40 ton. m/n sxhfc.... Installed in 98". I'm getting faults of o/a sensor fail and evap temp sense fail. Where are these sensors located in the unit. I'm reading the manuals as we speak and can't find anything. Tia Fitz
    Jan 2010
    Austin, TX
    O/A should be at the opposite corner of the unit from the Control Panel. That is if you are looking at the Control Panel, it would be to the left on the backside of the unit.
    Evap Temp Sensor is in the Blower section, just after the Coil.
    That is if my memory serves me right.
    Dec 2006
    new england
    Thanks for the help. Fitz
    Aug 2010
    Middle GA
    OA sensor is behind the mist eliminators / louvers at the back of the rtu in the outside air intake section. Evap sensor should be mounted to the suction line in the location sgraefe said.
    Home of the newly wed and the nearly dead
    Since these are older units, the evap temp sensor is located on the suction line in a well. The new 410a Intellipaks have an additional sensor on the distributor tubing for saturated evaporator temperature.
    Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
    "It's called the american dream because you have to be asleep to believe it" -George Carlin
    "A nation of sheep begets a government of wolves" -Edward R. Murrow
    "I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
    Buy american made goods & support locally owned businesses!
    Jun 2006
    midwest
    oas
    oas is ;located in the return air section behind the power exhaust term. boards and the evap sensor is located in the supply fan section on the suction line
    Dec 2006
    new england
    Thanks guys.