    help with dip switches- trane pkg unit

    Trane m#: Tch480a4oroa6kc5a
    How should the dip switches be setup on the rtam board.
    I would like to eliminate the ecomomizer from being used if possible.

  2. #2
    Join Date
    Apr 2005
    Location
    Boulder,CO.
    Posts
    559
    RTAM is for vav control, at the 4 wire plug on the econ. actuator just unplug it cycle power now it thinks it's an RTU without economizer.

  3. #3
    Join Date
    Aug 2010
    Location
    honolulu, hawaii
    Posts
    124
    Thx controldude!