    Copeland 3D, 4D RPM?

    Anyone know the typical RPM on a Copeland 3D,4D reciprocating compressor? Something in the back of my head is telling me 3450 RPM...but I cant remember for sure...1750 also comes to mind, but that seems too slow, more like a fan motor.

  2. #2
    Join Date
    Nov 2005
    Posts
    386
    3D 1370 rpm to 2127
    4D 2386 rpm to 3603
    6D 4136 rpm
    8D 6463 rpm to 7721

    Above min max readings depend on which model is being used

  3. #3
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,064
    Quote Originally Posted by -frozen-ocean- View Post
    3D 1370 rpm to 2127
    4D 2386 rpm to 3603
    6D 4136 rpm
    8D 6463 rpm to 7721

    Above min max readings depend on which model is being used
    Can you show me where you got these figures? I've been looking all day and seem to find 1750 everywhere.

    Thanks

  4. #4
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    4,354
    All Copeland semihermetics have 4 pole motors which means they run at 1750/1800 RPM. Welded compressors have 2 pole motors and run at 1450/3600 RPM. This is why semi hermetics make a deeper noise when running compared to welded hermetics which make a buzzing noise.


    If you ran any compressor at 7721 RPM, the parts on the inside would quickly be on the outside.

    On a side note, its not possible to run an induction motor above 3600 RPM on a 60 hZ source without a VFD

  5. #5
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,265
    I agree with craig1 on the RPM's.

    It appears -frozen-ocean-'s numbers are actually Copeland's compressor displacements in cu.ft/hr (CFH).

  6. #6
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    4,354
    Quote Originally Posted by craig1 View Post
    Welded compressors have 2 pole motors and run at 1450/3600 RPM.
    This was supposed to say 3450/3600 RPM

  7. #7
    Join Date
    Nov 2005
    Posts
    386
    Sorry for that, those are displacements in (CFH) not rpm.

  8. #8
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,647
    Quote Originally Posted by Phase Loss View Post
    Anyone know the typical RPM on a Copeland 3D,4D reciprocating compressor? Something in the back of my head is telling me 3450 RPM...but I cant remember for sure...1750 also comes to mind, but that seems too slow, more like a fan motor.
    Interesting question. What prompted this and how would a guy actually verify rpms?
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.

  9. #9
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,064
    Quote Originally Posted by engineerdave View Post
    Interesting question. What prompted this and how would a guy actually verify rpms?
    I was setting up some Copeland recip's to run on VFD's. And the VFD's motor parameter settings call for an RPM input.

    RPM's are not listed on the nameplate information.

    I knew there is a calculation for RPM= 120 X supply frequency(Hz) / number of poles

    I just didn't know how many poles are in Copeland's 3D, 4D recip's. It turns out there are 4 poles

    So 120 X 60Hz / 4 poles = 1800 RPM synchronous speed.

    However, induction run motors don't run 100% synchronous speeds, they have a slip...so the RPM is actually around 1750 for a 4 pole motor at 60Hz.

    It's some screw compressors that have 2 poles which run the 3450 RPM

  10. #10
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,647
    Huh. I'd heard that recips were being ramped up & down, don't recall that I've actually seen it anywhere outside the transport world, and they weren't using VFDs. How's it working out for you? The potential for energy savings could be very high, especially in supermarkets. Are you also using the stepper valves as well?
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.

  11. #11
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,064
    yeah it's on a supermarket rack system. 1 compressor per suction group. and they are using stepper valves too.

  12. #12
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,418
    Quote Originally Posted by Phase Loss
    yeah it's on a supermarket rack system. 1 compressor per suction group. and they are using stepper valves too.
    Only one compressor per group?

    Hmmm.

    No redundancy?

    I'm already not a fan.

  13. #13
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,064
    I mean, 1 compressor per suction group has a VFD. each suction group has at least 3 compressors total.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event