    Ice machine woes

    I have a manitowoc km-630 maf unit. It was unused for about a year and relocated. Upon firing the unit up, the potential relay clicks and stops and tries a few times. Run and start caps are good. The unit won't fire. I bought a hard start kit but I'm reluctant to use it because the setup already uses a hard start type setup. Any ideas what could be causing the compressor not to fire? I have checked everything. The only questionable part is pot relay. It's clicking. I'm thinking the compressor is locked up. Any advice?

  2. #2
    Join Date
    Jan 2008
    Posts
    125
    thats a hoshi number

  3. #3
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,308
    A KM-630 is a Hoshizaki crescent cube ice machine. If your relay is clicking, what is the amp draw? Are you sure the starting components are good? If so, compressor may be locked up. Replace the compressor.
    Every customer you take for granted today will be someone else's tomorrow.

  4. #4
    Join Date
    Sep 2008
    Location
    Cedar Rapids, IA
    Posts
    487
    Quote Originally Posted by DLZ Dan View Post
    A KM-630 is a Hoshizaki crescent cube ice machine. If your relay is clicking, what is the amp draw? Are you sure the starting components are good? If so, compressor may be locked up. Replace the compressor.
    Is it wired up to the correct voltage?

  5. #5
    Join Date
    Aug 2011
    Location
    west palm beach, fl.
    Posts
    2
    Check the compressor windings

  6. #6
    Join Date
    Jan 2005
    Location
    where it's nice and warm
    Posts
    276
    Take a simple amp reading of the three wires going to the compressor, it will tell you a lot if interpreted correctly.

  7. #7
    Thanks for the responses guys. Yes, it was a very frustrating night so yes, a convenient brainfart on my behalf. Yes it's a hoshi. Don't know what I was thinking. The compressor is shot. I pulled some of the refrigerant out and tapped on it as well as adding the hard start kit on top of factory stuff. It kicked on for about a second then slowed to a halt within another second or two. I wish I knew how the heck it got roasted from sitting for a year. It worked perfect before it was shut down. But it's become a parts machine now. Thanks alot for the thoughts. I'll try to return the favor sometime!

  8. #8
    Three post and you are posting the same link over and over.... this is what we call Spam.

    If you continue to post like this we will discontinue your account.


    thx

    Dad
    Last edited by Dad; 08-28-2012 at 12:51 PM.

  9. #9
    Join Date
    Sep 2008
    Location
    Pennsylvania
    Posts
    46
    Quote Originally Posted by bob_scheel View Post
    Is it wired up to the correct voltage?
    my first thought as well

  10. #10
    Join Date
    Sep 2011
    Location
    Plainfield IL
    Posts
    101
    I had a similar situation twice in my career that I can think of. The first time it happened the problem turned out to be low voltage. The second time it happened to me I replaced the relay and start components and still would not start. I new the compressor was not locked because it would shake at start up. It was a K body on springs. So what I did was, I measured the pickup voltage and picked up a Steveco relay that matched my measured pick up voltage and the compressor started up and ran fine.

  11. #11

    HoshizakiIce.com Name Change to BuyIceMachines.com

    Three post and you are posting the same link over and over.... this is what we call Spam.

    If you continue to post like this we will discontinue your account.


    thx

    Dad
    Last edited by Dad; 08-28-2012 at 12:51 PM.