    Confused Water in 80% furnace heatexchanger

    I just got back from a no heat call. Furnace is a 1993 Comfortmaker 80%, 150000 btu's. The basement is stone and very moist (mushrooms growing on the dirt floor).
    Furnace flue was very rusty, took the covers off and found a lot of moisture in the vestibule. Took the cover off the burners and found the tubes of the heat-exchanger filled with an 1 1/2" water. I figure it was caused by warm air circulating through the furnace during the summer and condensing in the heat exchanger. Also there is no A/C. I condemned the furnace and recommended replacement. This is the first time I have seen this. Does my theory of how it happened sound right? Also they never ran the blower during the summer.
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  2. #2
    Join Date
    Apr 2007
    Location
    Pa
    Posts
    758
    Post Likes
    We ha plant that has a sludge tower with a steel catwalk that has sludge below it. This building requires heat and the combination of moisture and the constant 45 degree air filledthe heat exchanger with water.

  3. #3
    Join Date
    Nov 2010
    Location
    Cincinnati, OH
    Posts
    221
    Post Likes
    I would guess the basement flooded. Is this rental property? Maybe the tenants didn't want to tell the land lord they flooded the basement some how. Was there any water in the blower?

  4. #4
    Join Date
    Jun 2009
    Location
    Nevada
    Posts
    139
    Post Likes
    Maybe you need to adjust the float ...

  5. #5
    Join Date
    Sep 2007
    Location
    Syracuse, NY
    Posts
    74
    Post Likes

    I ran across this on a rheem furnace 80%

    I ran acrossed this with a rheem furnace installed in a apartment building and found that the roof vent cover was off and caused the furnace to fill up part way with water. the furnace fired up and blew flames out the front of the furnace and fried all the controlls.
    Life is to short to sweat the little thing in life!

  6. #6
    Join Date
    Sep 2011
    Location
    Detroit MI.
    Posts
    1
    Post Likes
    ggtg

  7. #7
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    35,930
    Post Likes
    Coworker found this in Sis's Trane 80. We're going to look at it further tonight. It's in a cold, damp dungeon of a room in the lower level. Not sure what the answer is on in installation like this other than try to lower the RH in the room with a BIG dehumidifier.

  8. #8
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,163
    Post Likes
    Nope not a rental. This is my cousins new house. He was in it last winter and did not have a problem. This was my first time at his new house though.


    Quote Originally Posted by oldblue View Post
    I would guess the basement flooded. Is this rental property? Maybe the tenants didn't want to tell the land lord they flooded the basement some how. Was there any water in the blower?
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  9. #9
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    2,938
    Post Likes
    Dirt floor?

    Maybe some kind of vapor/moisture barrier can be put over it.
    I've discovered a natural law - everything gets progressively worse. Things only break down and become depleted. Life isn't worth living and everything is going to hell.

    Death is the messiah. Everything else is irrelevant and arbitrary.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Quality Home Comfort Awards