    No suction port??

    On this carrier chiller with four O6e, 2 tandem circuits and no gauge port on suction line. One of the circuits is going into low sat. alarm. Can I add refrigerant where I would add oil?

  2. #2
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,720
    How can you verify your chiller is low on charge without putting a guage on it? There should be a suction pressure port on the front of the compressor about the 3 o`clock position. But don`t go in thinking it`s low. Good Luck
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  3. #3
    Join Date
    Dec 2009
    Location
    Southern US
    Posts
    504
    Quote Originally Posted by BatesTech View Post
    On this carrier chiller with four O6e, 2 tandem circuits and no gauge port on suction line. One of the circuits is going into low sat. alarm. Can I add refrigerant where I would add oil?
    Is that temp or pressure! And if theres not a port on the suction service valve already there should be a plug where one can be added.
    I'm good at making things cold...You can ask my first two wives!

  4. #4
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,317
    If there's no gauge port on the suction line king valve, there will be a plug there where a port can be added. Do not add liquid refrigerant where the oil goes or in front of the compressor or you can damage the compressor.

  5. #5
    Join Date
    Mar 2011
    Location
    Houston
    Posts
    77
    Quote Originally Posted by R123 View Post
    If there's no gauge port on the suction line king valve, there will be a plug there where a port can be added. Do not add liquid refrigerant where the oil goes or in front of the compressor or you can damage the compressor.
    Thanks that's what I did I took the plug out and added a port. I new I could check pressure in the front but definitely not comfortable adding juice there. Thanks