    Sep 2011
    Souther Cal
    York YSBBBBSO-CFC Solid state starter
    Looking for advice, we have the York screw chiller that sounds locked up but the compressor spins freely, motor spins freely and meggs out good,and supply voltage to starter is normal. Does any one know if any parts on the starter are replaceble or do we have to replace the whole starter?
    Jun 2010
    U.A. (upper Alabama)
    Parts are replaceable. What fault is it showing?
    Sep 2011
    Souther Cal
    no fault
    It used put Trig OOL and now it tries to start but sounds like it is single phasing and then drops out motor amps were at 587% on display. But no fault on board.
    Sep 2011
    Souther Cal
    Quote Originally Posted by cperk View Post
    My tech wired every thing back up and it ran normal today could it be the trigger board or the parts that look like Igbt's
    Sep 2011
    Souther Cal
    Unit went off again on Motor controller external reset? any clues, we are thinking the trigger board is acting up.
    Aug 2000
    Austell, Ga.
    I am "Assuming" that you had to reset the Current Module inside the control panel....If so...Exactly what "Fault" was indicated. Overtemp???Overload?? etc..
    It would help to know why the CM2 shut the thing down..
    Ain't "None" of us as smart as "All" of us..