  1. #40
    Join Date
    Oct 2003
    Location
    las vegas
    Posts
    1,505
    had a big leaker last year & couldnt locate it with the insulated lines.
    i borrowed a thermographic camera from a plumber buddy & was lucky
    enough to find a cracked 90 in a liq. line within an hour.

  2. #41
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,647
    You said this was a Low Temp rack.... how many systems are Gas Defrost?
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.

  3. #42
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,671
    Quote Originally Posted by sprmktrefertech View Post
    I have never thought of checking the gas from the vacuum pump to indicate leaking ball valves...

    I'll give it a try next time I'm in that situation.

    If you are evacuating a system that held refrigerant, I will GUARANTEE you that your detector will alert on the exhaust. Even at 0 PSIG, what, exactly, do you think is contained within the piping?? Fruit juice?

    Quote Originally Posted by marvin View Post
    had a big leaker last year & couldnt locate it with the insulated lines.
    i borrowed a thermographic camera from a plumber buddy & was lucky
    enough to find a cracked 90 in a liq. line within an hour.
    Hmmmm.


    I've got on that I might need to look into this on one that I'm fighting right now.

  4. #43
    Join Date
    Jul 2005
    Location
    Southern California
    Posts
    585
    Quote Originally Posted by marvin View Post
    had a big leaker last year & couldnt locate it with the insulated lines.
    i borrowed a thermographic camera from a plumber buddy & was lucky
    enough to find a cracked 90 in a liq. line within an hour.
    thats a neat trick. never thought of that.

  5. #44
    Join Date
    Dec 2010
    Location
    new jersey
    Posts
    366
    [QUOTE=jpsmith1cm;11703452]If you are evacuating a system that held refrigerant, I will GUARANTEE you that your detector will alert on the exhaust. Even at 0 PSIG, what, exactly, do you think is contained within the piping?? Fruit juice?





    I will GUARANTEE you, if you read the reply correctly, you could have saved yourself from sounding obnoxious.

    This is an open forum....please refrain from child like behavior...and keep your fruit juice to yourself.

  6. #45
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,671
    As you said, this is an open forum.

    I try to pop foolish ideas like that when I see them. This is to prevent someone who isn't knowledgable from coming along and accepting them as being accurate.

    I apologize for offending you.

  7. #46
    Join Date
    Oct 2003
    Location
    las vegas
    Posts
    1,505
    Quote Originally Posted by pherman View Post
    thats a neat trick. never thought of that.
    plumber buddy came up with the idea & i had nothing to lose except for a couple of hrs. time. worked for us.

  8. #47
    Join Date
    Feb 2009
    Location
    Wisconsin
    Posts
    311
    I regularly leak check Walmart stores and have had many hard to find leaks. Even so, the toughest still only took 3 days repairs included. I use an Inficon Dtek Select detector. It has no problem finding even the smallest leaks with 404a. The worst was under a set of frozen bunkers. Had to separate and move them to get it fixed. Good luck.
    You have to fight through some bad days to earn the best days of your life.

  9. #48
    Quote Originally Posted by marvin View Post
    had a big leaker last year & couldnt locate it with the insulated lines.
    i borrowed a thermographic camera from a plumber buddy & was lucky
    enough to find a cracked 90 in a liq. line within an hour.
    Phase Loss has a thread where he has posted some very nice pics of what those cameras can do for us as a leak finder. Now to convince the company to buy one.

  10. #49
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,647
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.

  11. #50
    Join Date
    Feb 2009
    Location
    Wisconsin
    Posts
    311
    Sooooo..., you still workin on it? Cant just leave us hangin, where in circuit 2 was it?
    You have to fight through some bad days to earn the best days of your life.

  12. #51
    Join Date
    Sep 2011
    Location
    Tampa, FL
    Posts
    45
    Found 6 leaks with my new leak detector. 2 punctured evap coils and 6 suction line leaks. Coils have been replaced and all suction line leaks repaired. Thank god.

  13. #52
    Join Date
    May 2009
    Location
    The Pas, Manitoba Canada
    Posts
    212
    Don't want to be a pest but could you tell me which detector you have now.

Page 4 of 5 FirstFirst 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event