Results 1 to 10 of 10

Thread: clocking meter

  1. #1
    Join Date
    Dec 2004
    Posts
    24
    Post Likes
    for my own curiousity i clocked my gas meter, what would be my ratings in btu's .01 cubic meter dial 19 seconds per revolution the .05 cubic meter dial 111 seconds. the charts i checked show conversion for cubic feet only. thanks.

  2. #2
    Join Date
    Jan 2005
    Posts
    475
    Post Likes
    aprox.67000btuh

  3. #3
    Join Date
    Dec 2000
    Posts
    1,227
    Post Likes
    Btu per cu.ft. varies by region and their source of natural gas. In my area, about 1025 Btu/cu.ft.

  4. #4
    Join Date
    Oct 2003
    Location
    Florida's space coast
    Posts
    2,538
    Post Likes
    I know I'll probably hear about using the dreaded Rule of Thumb but 1000 btu's/cu. ft. will get you pretty close for an initial observation.
    We've been doing so much,for so long,with so little, that now we can do almost anything, with nothing at all.

  5. #5
    Join Date
    Nov 2003
    Posts
    51
    Post Likes
    another rule of thumb is every full revolution of the 1/2 ft dial on the gas mtr is 30,000 btu's. you clock the mtr for 1 minute 4 revs=120,000 btu's

  6. #6
    Join Date
    Dec 2004
    Posts
    24
    Post Likes
    Thread Starter
    my meter shows in cubic meters not cubic ft, on the charts i have seen the conversions are for cubic ft. this is where i'm stuck on finding the btu input.

  7. #7
    Join Date
    Jan 2005
    Posts
    475
    Post Likes
    I have a chart for clocking metric meters and as stated earlier on a .01 m3/rev test dial @ 19 sec/per rev you are looking at approx. 67 cubic feet /hour or 67000btuh ( based on 1000btuh/cubic foot)You can use the same formula for calculating input as you would on a standard meter using 3600 divided by the time for 1 revolution of your test dial and mutiplying by either .01 or.05 which will give you M3/HR. then multipy this by 10.35kWh/m3 which will give you the input in kilo-watts. Then knowing 1kw=3412btuh you can figure out the input.HTH

  8. #8
    Join Date
    Nov 2005
    Location
    Kansas City (zip 66204)
    Posts
    50
    Post Likes

    Will this help?



    1 cubic meter is ~35.3147 cubic feet.
    1 cubic foot is ~.02831685 cubic meeters.

    I don't know if that will help you or not, but I though that you mighr be able to convert you reading into cubic feet with that.

    Doug

  9. #9
    Join Date
    Dec 2004
    Posts
    24
    Post Likes
    Thread Starter
    Thanks to blk and dougjrs, thats the formula i was looking for.

  10. #10
    Join Date
    Jan 2005
    Posts
    149
    Post Likes
    Here is a link to a handy gas clocking calculator
    http://http://www.cozyparts.com/calc...gas_input.aspx