    Sep 2011
    Commercial Freezer Contacts question
    I have a commercial freezer that is not kicking on. Freezer is in store, compressor is on roof. When opening the compressor cabinet, I found a fan that had come off the shaft and had wedged into the motor. I re-installed the fan. The unit still did not respond. I checked capacitors for capacity and found one bad, replaced. Still no kick on. When power is applied, 240, slight tick from defrost control board. when I manually push in contacts, compressor and fans kick on. I checked voltage going to contact solenoid and it had voltage, 22vac. Ohms were 1.757 disconnected. I am guessing that the solenoid is bad on contacts. How did I do? Contact is Furnas 45CG20AG.
    Thanks guys
    I'm thinking your problem is a lot simpler than that.
    Look for a reset button.
    Sep 2011
    A reset button on the compressor? Please elaborate.
    Jim
    I'm not permitted to give you step by step instructions, nor am I going to.
    You were resourceful enough to repair a fan blade that came loose. That was the root cause of your problem.
    In the process, it is very likely that your unit went down on high pressure safety.
    Sep 2011
    Thank you
