I have a commercial freezer that is not kicking on. Freezer is in store, compressor is on roof. When opening the compressor cabinet, I found a fan that had come off the shaft and had wedged into the motor. I re-installed the fan. The unit still did not respond. I checked capacitors for capacity and found one bad, replaced. Still no kick on. When power is applied, 240, slight tick from defrost control board. when I manually push in contacts, compressor and fans kick on. I checked voltage going to contact solenoid and it had voltage, 22vac. Ohms were 1.757 disconnected. I am guessing that the solenoid is bad on contacts. How did I do? Contact is Furnas 45CG20AG.

Thanks guys