    I have a commercial freezer that is not kicking on. Freezer is in store, compressor is on roof. When opening the compressor cabinet, I found a fan that had come off the shaft and had wedged into the motor. I re-installed the fan. The unit still did not respond. I checked capacitors for capacity and found one bad, replaced. Still no kick on. When power is applied, 240, slight tick from defrost control board. when I manually push in contacts, compressor and fans kick on. I checked voltage going to contact solenoid and it had voltage, 22vac. Ohms were 1.757 disconnected. I am guessing that the solenoid is bad on contacts. How did I do? Contact is Furnas 45CG20AG.

    Thanks guys

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,674
    Post Likes

  3. #3
    Join Date
    Sep 2011
    Posts
    4
    Post Likes
    Thread Starter
    A reset button on the compressor? Please elaborate.
    Jim

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,674
    Post Likes
    I'm not permitted to give you step by step instructions, nor am I going to.

    You were resourceful enough to repair a fan blade that came loose. That was the root cause of your problem.

    In the process, it is very likely that your unit went down on high pressure safety.

  5. #5
    Join Date
    Sep 2011
    Posts
    4
    Post Likes
    Thread Starter
    Thank you