    electrical ? about contactor coils

    Every 24v contactor coil I ohmed out ranges between 8-11 ohms...new or atleast fairly new.

    I have one now thats showing 4 ohms.

    Im not going into the issue cuz I just wanna know if you agree wit an electrician on this one..

    He said .."its better to have a lower resistance cuz it gives higher amps..which creates a stronger magnetic field to pull contactor in stronger...."

    His reasoning is the p.i.e. formula....

    T or F
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton


    I'm learning all the time, the tombstone will be my diploma!!!


    Did you ever stop to think, and forget to start again?

  2. #2
    Join Date
    Aug 2011
    Location
    Ohio
    Posts
    53
    Post Likes
    I would want to know if the contactor in question is different than anything else you have seen. For example is this an exact same contactor as another one reading different resistance or is it a new contactor all together to you? Also there is a little more to resistance in A/C than just what you read with a meter. In a coil you get Inductive reactance which will cause current to lag voltage. This effects the Impedence which is defined by the total opposition to A/C current. This is also effected by the Plunger ( I hope that is the correct technical term) or the part inside that moves because of the magnetic field produced by the coil. An iron rod effects reactance and will cause a drop in current, for example: a solenoid valve that is stuck will cause the coil to burn up because since the valve didn't move the magnetic field doesn't have the stability it would if the valve was working properly.

    So I can't really answer your question but you would need to put the coil in a circuit and measure the current to calculate the resistance the circuit is actually seeing. I would compare them that way because I believe it would be more accurate. Although I am looking forward to someone with more knowledge to explain this.

  3. #3
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Stronger field? Yes.

    More current? Yes.

    More heat? Yes.

    Shorter life? Yes.

    Possible short in the windings? Almost certainly.

    Coils are designed with a certain effective wire length and reactance. There is no benefit for a coil in an identical application to have a lower resistance, as the 8 ohm coil (to use an example value) was already designed to have a field strength that is capable of pulling in the armature.

    A coil with a 4 ohm resistance will potentially tax the control breaker that feeds the unit, causing nuisance trips.

    If this resistance value is not the same as similar contactor coils, I'd change it out.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  4. #4
    Join Date
    Jun 2011
    Posts
    230
    Post Likes
    So at about what ohm reading do you say, ok it is time to replace it?

  5. #5
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    I'd try to compare pull-in and holding current to a typical unit and look for a 10-15% difference.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  6. #6
    Join Date
    Mar 2011
    Location
    Parker, Colorado
    Posts
    25
    Post Likes
    If you’re averaging between 8-11 ohms on similar contactors then 4 ohms is 50% of you lowest average I’d change it. It has been my experience 10 ohms is what I average.

  7. #7
    Join Date
    Sep 2011
    Posts
    29
    Post Likes
    Check its rating to make sure its the same coil as others and if its rated for 8 ohms but only has a resistance of 4 then i'd call it defective and trash it. It's not like its an expensive part and if your talking 3 phase, you dont want to chance anything with a faulty contactor.

  8. #8
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Dont mess with electricity bud ... when in doubt replace it

  9. #9
    Join Date
    Sep 2007
    Location
    NC
    Posts
    28
    Post Likes
    If the contactor Ohm reading should be closer to the OEM contactor for best operation.

  10. #10
    Join Date
    Jun 2011
    Posts
    230
    Post Likes
    What?

  11. #11
    Join Date
    Oct 2009
    Location
    St Pete, FL
    Posts
    76
    Post Likes
    Quote Originally Posted by Redwood650 View Post
    What?
    If the question is still at what ohm reading to replace, there's at least one experienced instructor who says replace every year at the annual inspection.
    Thus, if it isn't close to the reading of a new one, then as Timebuilder said, it's probably shorted. A short is going to WEAKEN the magnetic field, not strengthen it. I'd replace it.

  12. #12
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes

    Who would

    Quote Originally Posted by Bladeforger View Post
    If the question is still at what ohm reading to replace, there's at least one experienced instructor who says replace every year at the annual inspection.
    Thus, if it isn't close to the reading of a new one, then as Timebuilder said, it's probably shorted. A short is going to WEAKEN the magnetic field, not strengthen it. I'd replace it.
    this exsperienced instructor be?

  13. #13
    Join Date
    Oct 2009
    Location
    St Pete, FL
    Posts
    76
    Post Likes
    Quote Originally Posted by second opinion View Post
    this exsperienced instructor be?
    Henry Barclay, one of my instructors when I went to PTEC, who used to work at a big university (in the HVAC department). Their PM called for new contactors every year.

    And, yes, I know that they may work for a decade without failure; however, they do become pitted. They're cheap and easy to replace.

    Keith
    Last edited by Bladeforger; 10-06-2011 at 12:47 PM. Reason: add the info in parenthesis to be more clear

  14. #14
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    14,412
    Post Likes
    I've seen quite a few contactors in the last five or so years blow transformers because of shorted coils so if the resistance has dropped below half of normal I would replace it.
    Its going to draw more than twice as much amperage as the other ones so its much more load on the transformer. This is assuming your matching these numbers with the same type contactors.
    Gary
    -----------
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.
    When you appreciate what you have, you have a lot more.

  15. #15
    Join Date
    Dec 2000
    Location
    phoenix, arizona
    Posts
    1,149
    Post Likes

    Try this

    I often put a fuse holder in series with the low voltage transformer ( output- common), and I usually tape 2-3 spare fuse in a plastic bag attach to the fuse holder.


    http://www.ebay.com/itm/20X-In-line-...a#ht_500wt_969

    http://www.ebay.com/itm/ATC-ATO-BLAD...#ht_1415wt_952

    http://www.ebay.com/itm/ATC-ATO-BLAD...#ht_1415wt_952


    Tip: Many walk-in cooler have several evaporator motors, occasionally one will blow fuse intermittently (say-once a month), I put a fuse holder in line with each motor. Very easily identify intermittent motor. Work good for me.

    You maybe able to identify a bad contactor the same way.
    Decide what you want, decide what you are willing to exchange for it. Establish your priorities and go to work." H.L. Hunt

    "In order that people may be happy in their work, these three things are needed: They must be fit for it. They must not do too much of it. And they must have a sense of success in it." John uskin

  16. #16
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Bladeforger View Post
    If the question is still at what ohm reading to replace, there's at least one experienced instructor who says replace every year at the annual inspection.
    Thus, if it isn't close to the reading of a new one, then as Timebuilder said, it's probably shorted. A short is going to WEAKEN the magnetic field, not strengthen it. I'd replace it.

    Possibly.

    If the current can increase more than the decrease of wire length that is lost in the short, field strength can increase. That depends on how current is affected in the AC environment of the coil, and I don't have my books available to look at the likelihood of that.
    Last edited by timebuilder; 10-06-2011 at 06:28 PM.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  17. #17
    Join Date
    Oct 2008
    Location
    Nashville ,TN
    Posts
    546
    Post Likes
    Reset fuse so no need for fuses.

  18. #18
    Join Date
    Oct 2009
    Location
    St Pete, FL
    Posts
    76
    Post Likes
    Quote Originally Posted by timebuilder View Post
    Possibly.

    If the current can increase more than the decrease of wire length that is lost in the short, field strength can increase. That depends on how current is affected in the AC environment of the coil, and I don't have my books available to look at the likelihood of that.
    You might be right... what I was thinking was that IF it would work okay, then the manufacturers of contactors would be using shorter coils and saving $0.001 worth of copper. That they aren't was a "thinkin'-about-it" shortcut to reach a conclusion that the shorter coil isn't being used because it's not quite enough for reliability. Doesn't mean I came to a good conclusion for a right reason. The P-Nut relays, though, have a lot more resistance. They're about equally reliable as far as I know. So you may be right. Now I'm curious.

    Quote Originally Posted by Thomasg View Post
    Reset fuse so no need for fuses.
    Yes!!!

    Those 5A breakers are readily available, BTW, at Grainger. I had two supply houses give me squinty looks when I was in search of one, and the only thing in stock was part of a kit that cost about $20. I found 'em at Grainger for about $2. It's a Carling Technologies 4VA66 Carling Switch P/N CTB-B-B-05-XG.

    I've put in some UV germicidal lights and I have used a dedicated transformer that's kicked on by a separate relay off the green power. That way I put the smallest additional load on the original transformer and run the light only when the fan is moving air through the A/H. I wanted protection, but I didn't want a fuse. Thus the cheap 5A breakers. That way I'm SURE to not overload the original transformer. The breakers come with the males for push-on connectors.

    There's the part number and source if it helps anyone.

    Keith

  19. #19
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    In the case of p-nut relays...they have a higher impedance, and draw less power. They can close their low-current contacts reliably without a strong field, using less current for a given voltage.

    Stronger fields are needed to operate the larger (higher current) relays we call contactors. BUT, they have to do this without taking up too much power from the transformer secondary, because a larger transformer for the unit costs more to build. So, a shorted coil can sometimes remain functional and have the field strength needed to operate the contacts and armature, but the additional current draw is not optimal for most applications. Note that really large contactors use line voltages controlled by a pilot relay, because an increase in either I or E will give a larger VA value, and the needed field strength to operate the coil.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •