Thread: i need a 401b PT chart.
-
12-22-2005, 07:25 PM #1
ive been everywhere can someone supply me with one
i don't know why i use this stuff...
-
12-22-2005, 07:30 PM #2
http://www.refrigerants.com/pics/ptchart.pdf
401 at the end
A and B
12-22-2005, 09:05 PM #3R401B (MP66)...........
Here's another one.
I use it because it's the only one that works well for old R12 LT systems.
12-22-2005, 10:08 PM #4thanks guys..but somethings...weird..
i have a tp chart put out by tecumseh...
and it dosnt match what the honeywell chart says..
example..
techumseh mp39 @ 0*f =6.7 psi
honeywell mp39 @ 0*f =8.0 psi
hmmm? 22 was the same and 409 was real close..K-pasa?
am i spliting hairs?
12-22-2005, 10:17 PM #5the honeywell chart is the same as the one I gave you...
vapor pressure
12-23-2005, 07:13 AM #6Splitting another hair.......
DuPont's P/T chart shows 7.4 psig at 0ºF for R401A (MP39): http://refrigerants.dupont.com/Suva/...pdf/k10909.pdf