    Confused McQuay--High Head Pressure--Fan Cycling

    We have numerous McQuay Commercial Condensing Units--The First Condenser fan comes on Immediately--The setting for the second fan is 290 PSIG--Why so High--Would it have anything to do with the Compressor setup??--Tandem--Dual Circuit--Thank You.

  2. #2
    Join Date
    Aug 2010
    Location
    N.E Ohio
    Posts
    15
    Post Likes
    It is set this high for low ambient conditions so suction pressure can build up during the low ambient starts. Personally I have lowered this setting. If it is Micotech 2 {carel controller} the fan off/on can be set in fan setting page.