    Proper spacing of supply outlets off trunk

    What is the proper spacing between supply lines off the main supply truck?

  2. #2
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    5,094
    Quote Originally Posted by ace064 View Post
    What is the proper spacing between supply lines off the main supply truck?
    As tight as I need to get the stuff to fit.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  3. #3
    Join Date
    Sep 2011
    Posts
    11
    Is it better for two supply lines running to the same room to be close together or does that matter. Also, how does high or low air returns affect heating and cooling? It stands to reason that high returns work better in hot weather and low returns in cold weather. Which is best for both hot and cold weather?

  4. #4
    Join Date
    Aug 2008
    Posts
    416
    Before this discussion gets going (like all the previous high/low arguments) I have a question.
    Has there ever been a study where a room was set up with high and low returns and supplies and smoke was used to observe air mixing, stratification, etc...... Sure would be nice if someone knows of a scientific study with real measured data to provide a real answer... Just a thought...

  5. #5
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,837
    The height of supplies and returns is always a topic of hot conjecture but no matter the opinions of the panelists, warm air rises. What this means is that no matter the season, the warmest air is always high in the room. Thus positioning the returns high in the room serves to move the warmest air out and back to the equipment for treatment.

    In summer, it seems to be obvious that high returns are best but that seems to be lost on many when it comes to heating in winter. None-the-less, once the air has passed through a height of about 7-feet or that height in which people normally occupy, any further rise is wasted. Thus it is, whether the supplies are on the ceiling or the floor, warm air will exit the supply outlets and begin to rise. Since the very warmest air in the room will always be up at the ceiling, high returns are best.

    However there is one caveat to the location of supplies and returns. When a room has cathedral ceilings, it is not always wise to try and condition all of the room volume. It may be not only desirable but also necessary to ignore the highest parts of the room and allow the warmest air to be stagnant high up, thus allowing a 'reduced volume' of treated air below. Under some circumstances for cooling, the cool air could enter the room at very high ceilings and before it ever reaches the occupants below, it is mixed with warmer air and begins to ascend. This can result in a room that is uncomfortable even though Manaul 'J' loads indicate the room is adequately cooled.

    The one advantage to low floor returns is that much more dust and dirt will be removed from the rooms in which the return(s) are located.

  6. #6
    Join Date
    Aug 2008
    Posts
    416

    What About Flow

    Well that addresses the effect of temp..
    The other factor is the velocity and flow of air.
    If I have a heat vent in floor that is tending to throw the air upward, couldn't that be considered bad as warm air already rises, so throwing it upward only makes the problem worse. So one could imagine that in heat season you might want to throw from the celing downward while in cooling season you want to throw upward.. Thats why I was curious about any testing using smoke, etc.

  7. #7
    Join Date
    Feb 2008
    Location
    Waffleville
    Posts
    10,339
    Quote Originally Posted by wraujr View Post
    Well that addresses the effect of temp..
    The other factor is the velocity and flow of air.
    If I have a heat vent in floor that is tending to throw the air upward, couldn't that be considered bad as warm air already rises, so throwing it upward only makes the problem worse. So one could imagine that in heat season you might want to throw from the celing downward while in cooling season you want to throw upward.. Thats why I was curious about any testing using smoke, etc.
    please start a new thread

    it's not polite to hijack another posters thread.

    thanks
    If Guns Kill People, Do Pencils Misspell Words?

    http://www.youtube.com/watch?v=An2a1...eature=related

    Before we work on artificial intelligence why don't we do something about natural stupidity?

  8. #8
    Join Date
    Aug 2008
    Posts
    416
    No hijack intended, OP in Post #3 asked question about placement of returns and supllies, high and low. My comments were addressing air flow.

  9. #9
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,190

    Skip, nicely said

    Quote Originally Posted by skippedover View Post
    The height of supplies and returns is always a topic of hot conjecture but no matter the opinions of the panelists, warm air rises. What this means is that no matter the season, the warmest air is always high in the room. Thus positioning the returns high in the room serves to move the warmest air out and back to the equipment for treatment.

    In summer, it seems to be obvious that high returns are best but that seems to be lost on many when it comes to heating in winter. None-the-less, once the air has passed through a height of about 7-feet or that height in which people normally occupy, any further rise is wasted. Thus it is, whether the supplies are on the ceiling or the floor, warm air will exit the supply outlets and begin to rise. Since the very warmest air in the room will always be up at the ceiling, high returns are best.

    However there is one caveat to the location of supplies and returns. When a room has cathedral ceilings, it is not always wise to try and condition all of the room volume. It may be not only desirable but also necessary to ignore the highest parts of the room and allow the warmest air to be stagnant high up, thus allowing a 'reduced volume' of treated air below. Under some circumstances for cooling, the cool air could enter the room at very high ceilings and before it ever reaches the occupants below, it is mixed with warmer air and begins to ascend. This can result in a room that is uncomfortable even though Manaul 'J' loads indicate the room is adequately cooled.

    The one advantage to low floor returns is that much more dust and dirt will be removed from the rooms in which the return(s) are located.
    I AM IN YOUR CAMP!!!!!!!!!!
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  10. #10
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,851
    Ceiling fans are great at getting the warm air down to where the people are in winter.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  11. #11
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,334
    Low returns are fine for heating and cooling needs. The supplies have to installed properly, and chosen correctly. A floor register that only has a 5 foo throw, is not a good register for cooling needs when the ceiling is 8 foot above it.

    Many times a contractor will just figure they are going to get 100 CFM from a 6 inch round duct. When in truth, they are often barely getting 70 CFM. There can be a difference in throw of 4 foot between a register that has 70 CFM going through it, compared to a register that has 100 CFM going through it.

    High and low returns are ok to aid previous poor supply design, and register selection. But if your redoing the supplies, why not do them right.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #12
    Join Date
    Sep 2011
    Posts
    11
    wraujr- I do not feel highjacked at all. Keep sharing your ideas. We are all here to learn and share our experiences.
    Along these lines about high and low returns, is it proper to vent thru the 16 inch wide space between studs and place both high and low covers that are closeable. That way you can use the high one in summer and the low one in winter. The exit would be out the bottom area of the wall space into the air return trunk. Is this crazy or does it make sense?

  13. #13
    Join Date
    Aug 2008
    Posts
    416
    I have no advice or opinion. I bet this is one of those things you ask five pros and you get five different answers. But if some HVAC industry lab set up a test room with vents and smoke gens and a stack of calibrated thermomer every 12" in altitude, you'd get a proof positive answer and this would never be debated again (like it has on this site before). Thats why I asked if anyone knew of a study...

    I live in a house with floor vents and central return in hallway ceiling. I don't notice any layering/stratification, etc.
    I also work in a office with supply vents AND return in 9' ceiling and once again I notice nothing. I'd like to see science provide an answer...(with data please)

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event