    Hi Sargent york:
    really appreciate your reply,
    yes I believe the motor is a RAM motor,
    one of my customers in Vietnam has five YK chillers in their plant, all the five chillers are equiped with RAM motor, just in 8 years, they have 3 motors burned,
    and on the job site I currently work, there are another two same type chillers, their motor current also fluctuates, but no so serious, only have 2 or 3% differentials,
    I am not sure if I can give advice to the customer to replace the motor, because the motor had been working well for years, it seems the quality of RAM motor is so bad that it will eventually has problem someday.
    Attached Images Attached Images

  2. #15
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,606
    Have you done any leak testing on this Chiller ? if so have you fixed any problem areas ? , as mentioned before have you removed the charge ? if so how much did you get out in weight ? , because I believe you are short refrigerant.
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

  3. #16
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    when I was working in Vietnam, my colleagues have removed the refrigerant out of the chiller, the weight is estimated 500Kgs.
    we have done all the work you mentioned, the vacuum reading is 2000micron and it keeps the same after 24 hours.
    yes the chiller is short of about 100-120 Kgs R134a, and I am going to make the deficiency later.

  4. #17
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    I have talked to the operators, they told me when the current fluctuation just occurred, the chiller was still running in good condition, so I don't think the shortage of refrigerant is the cause, but still I will make up the deficiency first.

  5. #18
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,058
    Taicool, I understand your concern about advising a customer to replace a working motor. However, look at Klove's mention of a variac. That is an electrical tool or meter that is used to test a motor for an open rotor. Others on this site can probably provide you with info in how to perform this test. But I would first address other issues (low charge?) first. Trying to troubleshoot multiple problems is much easier and more accurate when done one at a time. And why not start with most obvious/easiest first?

  6. #19
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,610
    Are you absolutely certain that you don't have a loose vane or two that may be opening and closing erratically?

  7. #20
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Hi Nuclrchiller:
    I agree with you,
    I will charge refrigerant first, then proceed to other moves,
    about the variac, can you provide more information of it?

  8. #21
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Hi Klove;
    I have check every vane,
    I manually open the vanes, then shake them by hand,
    they all secured well.

  9. #22
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,296
    The "Variac" test the wisened KLove referred to is extremely easy on your version of the YK. I believe you have an EM starter with the six motor leads coming out at the bottom. Simply obtain a "Variac" from a electronic/electrical supplier, secure the power to the chiller, "Verify" all power has been secured, then connect the variac to any of the 3 motor windings (1-4, 2-5, 3-6) and apply up to 5 amps current monitored with a analog clamp-on ammeter and at the same time open the coupling cover and rotate the shaft "Slowly" while monitoring the applied current. A deviation in the applied current will prove an open rotor bar, or bars. The SB from Trane has you seriesing any of the 2 windings but I have "Never" had to resort to this on a motor the size you are dealing with as the Variac cannot supply the voltage/current (5-amps) needed.
    No need to remove refrigerant or undo the coupling, the test can be performed in less than 30 minutes on the Yorks...Much longer on any of the hermetics. The last Trane CVHF I was involved with had 13 open rotor bars. Verified with magnetic paper at the local motor shop.
    Ain't "None" of us as smart as "All" of us..

  10. #23
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Sir;
    I got it, that kind of instrument is easy to get in electronis shop, thanks for your explanation and instruction.
    also thanks Klove for providing the test method.
    Attached Images Attached Images

  11. #24
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,296
    Taicool.....
    I ain't no "Sir"....Just a recently retired old fart that still has some love for the game.
    Go Gettum' Tiger
    Ain't "None" of us as smart as "All" of us..

  12. #25
    Join Date
    Jul 2006
    Location
    The Great country of Texas
    Posts
    429
    Quote Originally Posted by RichardL View Post
    The "Variac" test the wisened KLove referred to is extremely easy on your version of the YK. I believe you have an EM starter with the six motor leads coming out at the bottom. Simply obtain a "Variac" from a electronic/electrical supplier, secure the power to the chiller, "Verify" all power has been secured, then connect the variac to any of the 3 motor windings (1-4, 2-5, 3-6) and apply up to 5 amps current monitored with a analog clamp-on ammeter and at the same time open the coupling cover and rotate the shaft "Slowly" while monitoring the applied current. A deviation in the applied current will prove an open rotor bar, or bars. The SB from Trane has you seriesing any of the 2 windings but I have "Never" had to resort to this on a motor the size you are dealing with as the Variac cannot supply the voltage/current (5-amps) needed.
    No need to remove refrigerant or undo the coupling, the test can be performed in less than 30 minutes on the Yorks...Much longer on any of the hermetics. The last Trane CVHF I was involved with had 13 open rotor bars. Verified with magnetic paper at the local motor shop.
    It's best if you push the current up to 10 amps instead of 4.5 like the bulletin suggest. Best way is to have an on-line analysis test done. It will tell you for sure if you have a bad rotor. The variac test sometimes will lie to you because the mass is not spinning. I have seen several have broke rotor bars that when cool, the will have continuity but hot, they pull apart. You might also look at it through vibration analysis. If you know the number of bars, you can check aceleration at "bar pass frequency". Yes, RAM motors are "value engineered!"
    "I'm from Texas, what country are you from?"

  13. #26
    Join Date
    Aug 2009
    Location
    Taiwan
    Posts
    63
    Sorry some mistake,
    The motor is actually a Toshiba motor,
    577Hp, FLA 776Amps, Ins Class F, S.F 1.0, LRA 5326 Amps,
    I plan to do the test with variac first, for the on-line analysis test, I have to ask a professional motor shop to help, because I don't have those related appliances and knoeledge,
    one more question, can you kindly suggest the proper specification of variac to be used in this kind of motor?

Page 2 of 6 FirstFirst 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event