    R123 carbon purge tanks

    Since Trane is no longer taking the carbon tanks back, what are you guys doing with them when they are full/out of date?
    Superheat, that must be REALLY hot.

  2. #2
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,067
    I always recommended to my customers to disconnect the full/out of date tank and piped the pumpout discharge directly to the rupture disc vent line. Paying to exchange that tank did nothing to help the chiller or the owner. Since Trane apparently no longer exchanges it , I'll be curious to see what the Trane techs here say. I'm thinking an awful lot of disconnected tanks are just sitting there on many of those chillers. Just make sure the vent line is piped according to the IOM so the drip leg can be checked periodically.

  3. #3
    Join Date
    Mar 2007
    Posts
    3,108
    I had an issue recently where the purge pumped out over 200 lbs. of R-123, there was 7 psig static pressure on the vent line from all of the liquid stacked up in there. Meanwhile, the chiller was running and there was -8 psig on the other side of the rupture disk. That's 15 psid; how the rupture disk didn't break and fill the machine with air, I'm not sure.
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  4. #4
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,610
    Quote Originally Posted by BergerMech Rob View Post
    I had an issue recently where the purge pumped out over 200 lbs. of R-123, there was 7 psig static pressure on the vent line from all of the liquid stacked up in there. Meanwhile, the chiller was running and there was -8 psig on the other side of the rupture disk. That's 15 psid; how the rupture disk didn't break and fill the machine with air, I'm not sure.
    There's a brace across the back of the disc. It's only rated to blow one direction, although it will break backwards if you get the pressure diff high enough. It would take quite a bit.

  5. #5
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,610
    Quote Originally Posted by turbomaster View Post
    Since Trane is no longer taking the carbon tanks back, what are you guys doing with them when they are full/out of date?
    Cut it in half, get the filler out, and scrap iron's going for about $.15 cents per pound. Get enough of 'em, you could pay for a vacation.......

  6. #6
    Join Date
    Oct 2009
    Location
    USA
    Posts
    48
    From a Trane tech: The carbon tank was the technology of the time. Now, this device resides within the purge. If you are keeping the existing purge and the purge time has saturated the tank, get rid of it. There is no code that says it is required as far as I know.

  7. #7
    Join Date
    Aug 2010
    Location
    Middle GA
    Posts
    104
    The Trane parts centers here were offering a $10 reward for saturated tanks that are returned. They do not require an exchange.

  8. #8
    Join Date
    Aug 2000
    Location
    USA
    Posts
    4,990
    Your poor planning does not constitute an emergency on my part!!!!

  9. #9
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    861
    Quote Originally Posted by Nuclrchiller View Post
    I always recommended to my customers to disconnect the full/out of date tank and piped the pumpout discharge directly to the rupture disc vent line. Paying to exchange that tank did nothing to help the chiller or the owner. Since Trane apparently no longer exchanges it , I'll be curious to see what the Trane techs here say. I'm thinking an awful lot of disconnected tanks are just sitting there on many of those chillers. Just make sure the vent line is piped according to the IOM so the drip leg can be checked periodically.
    I once opened a drip leg up and what I thought was water coming out, suddenly had a funny smell and eat the paint off of a 6 foot radius spot on the equip. room floor.

  10. #10
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    180
    Quote Originally Posted by lunchbox View Post
    The Trane parts centers here were offering a $10 reward for saturated tanks that are returned. They do not require an exchange.
    X2 and the promotion ends on 9-30.

  11. #11
    Quote Originally Posted by turbomaster View Post
    Since Trane is no longer taking the carbon tanks back, what are you guys doing with them when they are full/out of date?
    Not true, The carbon tanks can be returned to any Trane Parts Store and Trane Parts will accept them.

    Note: Trane recommends the tanks to be changed every 3 years or 4000 purge minutes from date of installation. Not changing the tanks as recommended, will result in unlawful refrigerant venting. Tanks should not be sitting around they need to be returned to Trane Parts for recycling.

  12. #12
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,063
    http://www.cryoline.ca/media/5_Canister_Kit.pdf

    Heres the Northern Guru's solution
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  13. #13
    Join Date
    Mar 2007
    Posts
    3,108
    Is there any reason you couldn't just wrap a heater around the purifier collection tank and put whatever refrigerant is in the tank right back into the chiller?
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event