How to check for duct air leakage
We are going to have our existing ducts sealed by contractor at same time as he installs new heat pump system. Ducts are in attic. Single return grille and 10 supply registers are in ceiling and walls.
If I had a way of measuring face velocity at each register and at return grille, would that give me an idea of how much leakage I have on existing system?
This would be a one time check, so I would need to use something like a low cost anemometer. Would that be accurate enough? Any suggestions for type?
-
09-15-2011, 11:50 AM #2
I don't think an anemometer would be accurate enough to detect a relatively small amount of leakage. Especially combining that error over all 10 registers. A flow hood would really be the most accurate way to measure the difference between return and supply. Not all that cheap though. This is something the contractor should have available.
-
09-15-2011, 12:09 PM #3
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
Your contractor should do a before and after for you. You are paying them to seal the ducts then they should be able to show you what you paid for.
-
09-15-2011, 12:35 PM #4
Regular Guest
- Join Date
- Aug 2011
- Location
- Kingston, Ontario
- Posts
- 195
They should, but duct sealing is just an add on to heat pump installation, so sealing is not their main focus - just going to assign a helper to work on them while they are here.
Maybe after the new system is in and before we complete attic insulation (which will cover ducts), I will have leakage checked. I have to have a second house audit done (to qualify for rebates) so maybe we can learn something from that? Maybe do blower door test with and without openings covered?
Perhaps I could buy a hand held anemometer, just to check relative flows from registers? Might help in balancing?
-
09-15-2011, 02:37 PM #5
well, you can usually rent flow hoods (80+/day, probably).
-
09-15-2011, 12:22 PM #6
Professional Member*
- Join Date
- Feb 2010
- Location
- Cal
- Posts
- 1,323
Anemometer? No, useless. The testing equipment will cost you a couple G's.
-
09-15-2011, 02:50 PM #7
Professional Member*
- Join Date
- May 2004
- Location
- south louisiana
- Posts
- 2,192
or when you schedule the blower door test
schedule a duct blaster test.
have hvac company there to see what they
missed in sealing ducts & re-seal.
mark actual leakage sites instead of just
getting equiv leakage area
best of luck.The cure of the part should not be attempted without the cure of the whole. ~Plato
-
09-15-2011, 07:28 PM #8
Professional Member*
- Join Date
- Jun 2010
- Location
- Philadelphia PA
- Posts
- 2,139
Great answer from Energy Rater
And hope they also understand airflow duct sizing and designor when you schedule the blower door test
schedule a duct blaster test.
have hvac company there to see what they
missed in sealing ducts & re-seal.
mark actual leakage sites instead of just
getting equiv leakage areaYou have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!
-
09-15-2011, 08:18 PM #9
Regular Guest
- Join Date
- May 2008
- Location
- Picayune Ms.
- Posts
- 23
Duct sealing and new unit
This is a costly investment to your home that should last for years. Verify you have picked the RIGHT contractor and/or get other quotes.
-
09-16-2011, 10:01 AM #10
Regular Guest
- Join Date
- Aug 2011
- Location
- Kingston, Ontario
- Posts
- 195
I did get several quotes and chose the company which I felt most confident with. They were also recommended by other companies who couldn't do the Mitsubishi install for me. They are a commercial company very well thought of in our area - not a fly by nighter

Other than confirm the duct sizing is OK for the new unit, the existing ducts are not their main responsibility. They are just supplying a helper to seal as best they can where existing ducts are accessible. New ducts will be properly sealed.
All I wanted to do myself was see if there was a simple method to get a measure of how much of an improvement the duct sealing will make - a before & after.
-
09-16-2011, 10:15 AM #11
Professional Member*
- Join Date
- May 2004
- Location
- south louisiana
- Posts
- 2,192
make sure that the helper is on the right page.
mastic seals only..not duct tape or caulks
(hvac caulk is ok..don't like it personally but...)
mastics are paint on..in a bucket applied with a brush
and mastic tapes..sticky gray backing, not foil only tape
pleunm to equipment joints
duct take offs to plenum
duct to supply box
and lastly mastic sheetrock (ceiling) to supply box.
this often requies flex duct being taken off collars
to seal completely and 3/4 around collar to plenum.
inner liner mastic sealed,
insulation and outer liner in full contact with plenum/supply box
and mastic sealed.
its a bit more that as best as they can where accessable.
it is worth making access.
new construction duct leakage nation wide averages 25%
existing homes higher. its a big deal.
best of luckThe cure of the part should not be attempted without the cure of the whole. ~Plato
-
09-16-2011, 02:58 PM #12
Keeping in mind, of course, that duct leakage in UNCONDITIONED space is the bad part. duct leakage into walls that are only venting into the conditioned space is not of much concern, as well as in-between floor spaces.
-
09-17-2011, 10:50 AM #13
Professional Member*
- Join Date
- Jun 2007
- Location
- Round Rock
- Posts
- 2,890
The ONLY way to tell duct leakage is the duct blast tester. There is nothing you can do yourself except write a check to somebody who does this. Usually it costs a couple of hundred dollars to have it done. Kinda scary a commercial company is doing the install. Sounds like business is slow and they're looking for other revenue sources. Could be good or really bad for you.
I like DIY'ers. They pay better to fix.