    Constant Fan option ( 355 Bav Bryant )

    Constant Fan needs to be adjusted on a 355 bav/cav 3-stage furnace to a nice LOW setting for 24/7 air purification ~

    Thermostat is a standard Honeywell Pro600

    We all know with an Evolution Stat you can easily adjust LOW/MED/HIGH but with a non communication you can ( I say can as I'm assuming ) adjust the CF dip switches.

    I'm experiencing no luck...

    SW1 bank ( 1 thorough 8 ) dip switch 5 is set to Manual a/c or CF
    CF bank when set to 525 CFM or 700 CFM the fan doesn't change one bit, sounds like a JET and the blower tonnage is 42....

    Has anyone adjusted the Constant Fan speed for those customers with a standard thermostat who would like to move air flow 24/7 at a lower speed ?

    Thanks
    I forgot my Pen !!!

    Quote Originally Posted by RoBoTeq View Post
    Think of the old stuff as dumb and strong and the new stuff as smart but just not so tough.

  2. #2
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Try this procedure:

    Continuous Blower Speed Selection from Thermostat

    To select different continuous-blower airflows from the room thermostat, momentarily turn off the FAN switch or push-button on the room thermostat for 1-3 seconds after the blower motor BLWM is operating. The furnace control CPU will shift the continuous-blower airflow from the factory setting to the next highest CF selection airflow. Momentarily turning off the FAN switch again at the thermostat will shift the continuous blower airflow up one more increment. If you repeat this procedure enough you will eventually shift the continuous blower airflow to the lowest CF selection. The selection can be changed as many times as desired and is stored in the memory to be automatically used following a power interruption.

    This is from the service manual.
    Instead of learning the tricks of the trade, learn the trade.

  3. #3
    Join Date
    Nov 2005
    Location
    Milwaukee, WI
    Posts
    279
    Post Likes
    Thread Starter
    I did just that and nothing different happened...

    As we speak all of the Dip switches are in Default aka off for the CF or A/C
    I forgot my Pen !!!

    Quote Originally Posted by RoBoTeq View Post
    Think of the old stuff as dumb and strong and the new stuff as smart but just not so tough.

  4. #4
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    What is the full model number?

    With the CF switchs off - the default airflow is either 1050 cfm or 1750 cfm
    Instead of learning the tricks of the trade, learn the trade.

  5. #5
    Join Date
    Nov 2005
    Location
    Milwaukee, WI
    Posts
    279
    Post Likes
    Thread Starter
    I think it was 355BAV042060

    Yes with them off it sounded like a god dam JET !!!

    The subject about CF was brought up for comfort and he said " Its to dam loud " to run. I said no way put it on low ( I'm used to Evolution Control setting it to LOW ) and your good to go...
    I forgot my Pen !!!

    Quote Originally Posted by RoBoTeq View Post
    Think of the old stuff as dumb and strong and the new stuff as smart but just not so tough.

  6. #6
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Is this a two stage thermostat and 2 stage cooling?

    The Air Conditioning Relay Disable Jumper (ACRDJ) on the board must be disconnected to allow thermostat control of the outdoor unit staging, and If I'm not mistaken, the blower motor also.
    Instead of learning the tricks of the trade, learn the trade.

  7. #7
    Join Date
    Nov 2005
    Location
    Milwaukee, WI
    Posts
    279
    Post Likes
    Thread Starter
    Quote Originally Posted by rundawg View Post
    Is this a two stage thermostat and 2 stage cooling?

    The Air Conditioning Relay Disable Jumper (ACRDJ) on the board must be disconnected to allow thermostat control of the outdoor unit staging, and If I'm not mistaken, the blower motor also.
    1 stage Pro 6000
    1 stage A/C
    355bav is 3 stage...
    I forgot my Pen !!!

    Quote Originally Posted by RoBoTeq View Post
    Think of the old stuff as dumb and strong and the new stuff as smart but just not so tough.

  8. #8
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Other than making sure the tstat is sending out 24v on "G" to the board during continuous fan, I'm out of ideas.

    You might try resetting the entire unit - power off and re-selecting dip switches to make sure you don't have one sticking.

    May be time to call Carrier Tech support and see what they say. Might be a board issue.
    Instead of learning the tricks of the trade, learn the trade.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •