    TRANE CENTRAVAC

    WHAT WOULD BE CONSIDER NORMAL 24 HRS PURGE RUN TIME FOR NEW 750 TON TRANE CENTRAVAC

  2. #2
    Join Date
    Aug 2010
    Location
    Middle GA
    Posts
    104
    If the chiller is running, and the purge mode is set to "auto", then the purge will run as long as the chiller is.
    If you mean the purge pumpout time in a 24 hour period, I always use more than about 20-30 minutes a day as the cutoff point and think that it is significant enough to perform a leak check on the chiller. (assuming it can be taken down long enough for that)

  3. #3
    Join Date
    Sep 2011
    Location
    Brooklyn NY
    Posts
    3
    I was referring to 24 hrs pump out period max purge alarm setting.

  4. #4
    Join Date
    Oct 2009
    Location
    USA
    Posts
    48
    Normal is 0 min. Purging more than 10 min a day is time to start looking for a leak or at least go over all the flat gaskets.

    Setting the max pump out to something like 10-20 min is normal.

  5. #5
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,067
    Unless the chiller is so new it was just started up. Then there could be air introduced during charging. If that is the case give it a day or two (with chiller running) for the purge to remove that air. I'm just curious, but did you ask the Trane tech who started it?

  6. #6
    Join Date
    Sep 2004
    Posts
    522
    maximum pumpout for 24 hours comes set at 10 mins from factory

  7. #7
    Join Date
    Aug 2007
    Location
    Dallas Area
    Posts
    20
    10 - 20 min. this setting is just to let you know if you develop a leak in the machine. in the event you do develope a leak the max pump out alarm will flash to let you know, that you have an issue

  8. #8
    Join Date
    Sep 2011
    Location
    Brooklyn NY
    Posts
    3
    Thanks to all

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event