converting 0-10 vdc signal to 4-20 ma signal
Hi,
I need to ask if some one has ever converted 0-10vdc signal to 4-20 ma signal.. has anybody tried this my sensor is giving 0-10 vdc output but my controller accepts 4-20 ma signal...
-
09-13-2011, 02:34 PM #2
Removed by Admin- No Return
- Join Date
- Aug 2009
- Posts
- 2,459
What is the impedance of the input?
Can it accept a 0-20ma signal, or only a 4-20ma signal?
-
09-13-2011, 02:47 PM #3
Resistor
On the Johnson AHU controllers they use
1. You use 250ohm for 5 VDC and 500ohm for 10 VDC
2. This gives you a 0 to 20 ma signal
-
09-13-2011, 02:50 PM #4
Regular Guest
- Join Date
- Nov 2009
- Location
- karachi
- Posts
- 174
-
09-13-2011, 02:54 PM #5
Regular Guest
- Join Date
- Nov 2009
- Location
- karachi
- Posts
- 174
-
09-13-2011, 03:00 PM #6
Removed by Admin- No Return
- Join Date
- Aug 2009
- Posts
- 2,459
It's a whole lot easier to convert a current to a voltage than it is the other way around.
It would seem that you are saying that you need to scale the signal (0-100% to 20-100%) in addition to changing it from voltage to current. If that truly is the case, you can't just fix everything with a resistor- you're in need of a op-amp circuit of some sort.
-
09-13-2011, 03:06 PM #7
Regular Guest
- Join Date
- Nov 2009
- Location
- karachi
- Posts
- 174
-
09-13-2011, 03:09 PM #8
Regular Guest
- Join Date
- Nov 2009
- Location
- karachi
- Posts
- 174
ok suppose if I need 0-10 vdc to 0-20ma then what can I do??[QUOTE=BACnet;11271172]It's a whole lot easier to convert a current to a voltage than it is the other way around.
It would seem that you are saying that you need to scale the signal (0-100% to 20-100%)
-
09-13-2011, 03:13 PM #9
Removed by Admin- No Return
- Join Date
- Aug 2009
- Posts
- 2,459
In a word- No.
You still haven't given us the impedance information which is the most important thing in this entire thread. Not having seen it though, I can still say that the answer is "No." A resistor network is not going to scale/condition your signal and also boost up the power of the signal enough to achieve 20ma across the input.
Are you absolutely sure that the board will only read in a 4-20ma signal? What brand makes an analog input that can't be configured?
If that really is the case, you could always tear out the input resistors (which convert the current signal to a voltage signal that the ADC reads) and replace them with a set that will look at the voltage directly.
But that would violate all of the certifications for the device and most likely the warranty.
-
09-13-2011, 03:14 PM #10
Removed by Admin- No Return
- Join Date
- Aug 2009
- Posts
- 2,459
-
09-13-2011, 03:18 PM #11
Regular Guest
- Join Date
- Nov 2009
- Location
- karachi
- Posts
- 174
-
09-13-2011, 03:26 PM #12
Removed by Admin- No Return
- Join Date
- Aug 2009
- Posts
- 2,459
The input impedance. Of the controller's analog input. That's the information we need to continue this discussion.
Of course if it's a BACnet controller you can attach the sensor to a better controller (one that can handle other sorts of AI's) and then map the data over to this controller's AI via network writes. Of course you have to set the "Out of Service" property to "true" on the overridden AI to allow it to take the write.
-
09-13-2011, 03:33 PM #13
Removed by Admin- No Return
- Join Date
- Aug 2009
- Posts
- 2,459
According to this PDF, TAC humidity sensors can be set to put out 0-10 or 4-20.
Looks like this is a non-issue...