Thread: Suction meltaway relief valve open

  1. #1
    Join Date
    Jul 2006
    Location
    North Jersey
    Posts
    129
    Post Likes

    Suction meltaway relief valve open

    Got a service call on a Carrier condenser that wasn't working. Found the suction meltaway relief valve open, and the entire charge gone.

    Condenser fans seem to be working, and everything else control wise seems to be working. Not sure how this let go, and never seen a suction one let loose before. No one was soldering near this thing or anything like that.

    Wondering if any of you guys have seen the same, and what the apparent cause may be.

    It's about a 20-ton condenser with a recrip compressor.

    Thanks,
    MJB
    I like turbos

  2. #2
    Join Date
    Feb 2006
    Location
    Atlanta,GA.
    Posts
    1,024
    Post Likes
    yes I have seen that happen on some older units probably have bad valves and compressor got hot and released refrigerant some did not have over temp cut outs on them especially on rebuilt compressors or some one bypassed or removed them

  3. #3
    Join Date
    Jul 2006
    Location
    North Jersey
    Posts
    129
    Post Likes
    Thread Starter
    The unit is not old at all (maybe 5 years)...And these reliefs were not on the compressor, but about 2 feet away on the suction piping. Carrier says the suction one melts at 176 deg F, liquid at 210 deg F.

    Can't see how the suction got that hot, that far away.

    Maybe just a faulty plug? Just didn't know if there was a reason that the suctions melt? Never had one fail before.

    Compressor still seems good, but we'll see.
    I like turbos

  4. #4
    Join Date
    Feb 2006
    Location
    Atlanta,GA.
    Posts
    1,024
    Post Likes
    dont think they put the overtemp protector on them any more 06s but yes they will get that hot on the suction with bad valves

  5. #5
    Join Date
    Jul 2006
    Location
    North Jersey
    Posts
    129
    Post Likes
    Thread Starter
    Quote Originally Posted by chillerout1 View Post
    dont think they put the overtemp protector on them any more 06s but yes they will get that hot on the suction with bad valves
    But we'd see some indication of that by the pressures, no?
    I like turbos

  6. #6
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by turbo50mike View Post
    But we'd see some indication of that by the pressures, no?
    And what pressures would that be?

  7. #7
    Join Date
    Jul 2006
    Location
    North Jersey
    Posts
    129
    Post Likes
    Thread Starter
    Quote Originally Posted by thegoodlistener View Post
    And what pressures would that be?
    Suction pressures. I would imagine that we would see an increase in suction pressures/temperature if the valves were shot. How else would it melt that 176 deg F plug on the suction line?
    I like turbos

  8. #8
    Join Date
    Oct 2008
    Posts
    8
    Post Likes
    I would imagine faulty capacity control valve,unloader

  9. #9
    Join Date
    Feb 2006
    Location
    Atlanta,GA.
    Posts
    1,024
    Post Likes
    yes you would see higher than normal pressures

  10. #10
    Join Date
    Nov 2009
    Location
    Saskatchewan
    Posts
    494
    Post Likes
    I hear UV light from the sun breaks them down. No more ozone layer where you live.

    HAHAHAHAHAHa Now to be serious.

    I had one let go in a fire once. Good thing the R22 put out the fire and saved the building.
    I would suspect you just have a bad one, they are just super soft solder. Bad joint. I have done a few that just let go for no reason. Was this an Aquasnap by chance?

  11. #11
    Join Date
    Dec 2005
    Posts
    2,032
    Post Likes
    I have them idiotic plug. I normally take them out. And use some thing else to protect the system or compressor.

    I cannot believe that EPA still allow carrier to use this type of method to relief 100 of lbs of R-22 in to the atmosphere. I guess they got money to buy the EPA.

  12. #12
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Got a model number for that Carrier ?

  13. #13
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by just_opinion View Post
    I have them idiotic plug. I normally take them out. And use some thing else to protect the system or compressor.

    I cannot believe that EPA still allow carrier to use this type of method to relief 100 of lbs of R-22 in to the atmosphere. I guess they got money to buy the EPA.
    What type of alternative do you use?

  14. #14
    Join Date
    Mar 2001
    Location
    Ilwaco, Washington
    Posts
    1,638
    Post Likes
    On commercial fishing boats I use a PRV piped to the suction side of the compressor. Install a flow switch and a sight glass. Hook the flow switch up to an alarm, and then the engineer is notified of a problem without the loss of refrigerant. Found one, one time that was piped in a green garden hose to the air inlet of the auxillary engine. If the prv opened due to failure of the condenser pump, the refrigerant flowed into the air intake of the engine, and caused pretty white smoke to come out of the exhaust pipe on deck, notifying the operator of a problem in the engine room. LOL
    One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........

  15. #15
    Join Date
    Dec 2005
    Posts
    2,032
    Post Likes
    Quote Originally Posted by thegoodlistener View Post
    What type of alternative do you use?
    For the suction line to get that hot to melt the soft-plug, the discharge line must be VERY hot too. So use temp switch.

    Also, if the soft-plug is melted at (someone claimed) 160 degrees F, then why not use a temperature switch. Rather than releasing 100 lbs of R-22, which EPA said depleting the ozone, into the sky.

    Carrier uses this method on other types of applications too, such as residential units with reciprocated compressor, today new scroll compressor, today chiller with scroll. In fact they use this on all of their applications.

    Who cares, I don't own these machine. I work on them.

  16. #16
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Quote Originally Posted by just_opinion View Post
    Who cares, I don't own these machine. I work on them.

    My guess is that the plug is full proof and mechanical controls could fail resulting in a worse case scenario

  17. #17
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by VTP99 View Post
    My guess is that the plug is full proof and mechanical controls could fail resulting in a worse case scenario
    Or be bypassed.

  18. #18
    Join Date
    Jul 2007
    Location
    New Jersey
    Posts
    3,035
    Post Likes
    Had 2 ...one last year on suction line.

    It was a Carrier water cooled package unit.

    Couldnt believe the same thing..SUCTION THAT HOT...???

    Ended up with a cracked condenser and water breach...Hooked nitro and water shot out like a hydrant!! Not sure which happened first in that case..the water breach or the heating of the system...CHICKEN OR THE EGG?

    Last month i had a aircooled rooftop package...LL thermal plug blew open.

    Ended up with a grounded compressor.

    This was a result of a bad condenser fan motor and bad high pressure switch.

    I have no idea why have one on the suction line. Matter fact these old 50BR units dont have any on the LL, only suction....DONT ASK CUZ I CANT ANSWER.
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton


    I'm learning all the time, the tombstone will be my diploma!!!


    Did you ever stop to think, and forget to start again?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •