Got a service call on a Carrier condenser that wasn't working. Found the suction meltaway relief valve open, and the entire charge gone.
Condenser fans seem to be working, and everything else control wise seems to be working. Not sure how this let go, and never seen a suction one let loose before. No one was soldering near this thing or anything like that.
Wondering if any of you guys have seen the same, and what the apparent cause may be.
It's about a 20-ton condenser with a recrip compressor.
Thanks,
MJBI like turbos
-
09-13-2011, 09:00 PM #2
Professional Member*
- Join Date
- Feb 2006
- Location
- Atlanta,GA.
- Posts
- 729
yes I have seen that happen on some older units probably have bad valves and compressor got hot and released refrigerant some did not have over temp cut outs on them especially on rebuilt compressors or some one bypassed or removed them
-
09-13-2011, 09:07 PM #3
The unit is not old at all (maybe 5 years)...And these reliefs were not on the compressor, but about 2 feet away on the suction piping. Carrier says the suction one melts at 176 deg F, liquid at 210 deg F.
Can't see how the suction got that hot, that far away.
Maybe just a faulty plug? Just didn't know if there was a reason that the suctions melt? Never had one fail before.
Compressor still seems good, but we'll see.I like turbos
-
09-13-2011, 09:20 PM #4
Professional Member*
- Join Date
- Feb 2006
- Location
- Atlanta,GA.
- Posts
- 729
dont think they put the overtemp protector on them any more 06s but yes they will get that hot on the suction with bad valves
-
09-13-2011, 09:26 PM #5
-
09-13-2011, 10:42 PM #6
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,510
-
09-14-2011, 02:58 PM #7
-
09-15-2011, 10:16 PM #8
Regular Guest
- Join Date
- Oct 2008
- Posts
- 8
I would imagine faulty capacity control valve,unloader
-
09-17-2011, 12:25 AM #9
Professional Member*
- Join Date
- Feb 2006
- Location
- Atlanta,GA.
- Posts
- 729
yes you would see higher than normal pressures
-
09-17-2011, 12:39 AM #10
I hear UV light from the sun breaks them down. No more ozone layer where you live.
HAHAHAHAHAHa Now to be serious.
I had one let go in a fire once. Good thing the R22 put out the fire and saved the building.
I would suspect you just have a bad one, they are just super soft solder. Bad joint. I have done a few that just let go for no reason. Was this an Aquasnap by chance?
-
09-17-2011, 02:37 PM #11
Professional Member*
- Join Date
- Dec 2005
- Posts
- 1,655
I have them idiotic plug. I normally take them out. And use some thing else to protect the system or compressor.
I cannot believe that EPA still allow carrier to use this type of method to relief 100 of lbs of R-22 in to the atmosphere. I guess they got money to buy the EPA.
-
09-17-2011, 02:54 PM #12
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
Got a model number for that Carrier ?
-