09-13-2011, 09:32 AM #1
equal friction vs velocity
Ok so I think I'm right but I'm around so much that is wrong I might be hurting my confidence. Everyone here is screaming that I should be creating ducting at .1 friction per 100'.....which is fine...but on a 4 ton system thats putting me at 1100 fpm....From everything I know thats awfully high, isn't it?
I design it for 700 fpm(especially bc the client complained about noise)....granted that takes me down to.03....but i dont see that as a bad thing...just means i have a 20x18 duct. wont i lose a LOT at 1100 fpm?
Am I an idiot (for this reason specificially) or are they right?
-
09-13-2011, 11:13 AM #2
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
invest in ear plugs. 0.1 is to high try 0.06 for your supply
-
09-13-2011, 12:30 PM #3
the difference you need to look at is Trunk versus Branch ductwork.... I have always designed my ductwork by velocity and have never gotten in trouble yet but I also designed my TRUNK Ductwork at different velocities then my BRANCH ductwork.... my Ext. Statics have always been great at no noise issues.... I also stop using DUCTULATORS they sux. try this formula---- duct sq.ft. x fpm or (radius sq. x pi)/144 x fpm example - 10 inch flex = 78.53982 sq.in./144 = 0.545415 sq.ft. x 500 fpm = 272.7077 cfm
If you don't know... ASK!
-
09-13-2011, 12:53 PM #4A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii
-
09-13-2011, 01:11 PM #5
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
Not knowing how to use one!!!
-
09-13-2011, 01:12 PM #6
flex duct does come in 9" it is the last odd diameter it does come in but I like even numbers too... lol
If you don't know... ASK!
-
09-13-2011, 01:16 PM #7
no I have mastered using ductulators it is just much easier not having to run to another device when I can just do the math in my head...
If you don't know... ASK!
-
09-13-2011, 03:36 PM #8
It's funny, the different opinions on friction. I was taught to use .08" for supply and .07 for return. I have spoken with some who use .1" for supply and .08" for return. Now, I see someone using .06". I guess as long as velocity is kept below 1000 fpm and a suitable amount of static pressure is generated, a system will work reasonably well?
I've also known people, when using nothing but 6" pipe for the branches, will count the number of runs, multiply by 2 and add 2 to get the width of an 8" rectangular duct. For example: a house with 12 runs 12X2=24 24+2=26, so an 8X26 duct would be needed.A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii
-
09-14-2011, 08:01 AM #9
arghhhh...i really need to take that nci course on air balancing...
so .08 at 1600 cfm still puts me at 1000 fpm....so again...whats wrong with 700fpm? shouldnt it be whisper quiet??
-
09-14-2011, 09:17 AM #10
700 fpm would be quiet. However, with that low of friction, I would be concerned about the systems ability to generate enough pressure to give you good airflow out your registers.
A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii
-
09-14-2011, 09:43 AM #11