    Fan efficiency due to "crud"

    It's only logical that a fan loses efficiency as it ages and airborne crap (technical term) accumulates on the insides of the fan. Are we talking 2%-5% loss of efficiency or are we possibly talking 10% (more?).
    I have inherited a Trane Voyager that I'm having a static problem with, I am down about 15% from when the unit was first commissioned, duct work looks tight and i am tempted to re-sheave, just wondered if there was any insight from the group, before i do anything. The consensus among my Tech friends is that it would only have negligible affect, is there any reference material out there?

    ..john

  2. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    8,494
    Post Likes
    it's been a long time since I was informed of efficiency decline, but I'm thinking something along the line of 8-10 % reduction in air flow with the slightest film on blower vanes.

    someone will correct me shortly
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #3
    Join Date
    Dec 2009
    Location
    Bristol NH
    Posts
    229
    Post Likes
    I was told by a manufacturers instructor at a course that if the blade is 5-10% filled it will decrease performance by up to 25%. Take an amp reading before and after cleaning each blade Ans you will see the differance.

  4. #4
    Join Date
    Jun 2011
    Location
    Houston area
    Posts
    1,493
    Post Likes
    It will dramatically affect airflow, especially if it is a forward curved centrifugal wheel in a Archimedic scroll housing. It can be easily 25% or more depending on the amount of crud.
    The picture in my avatar is of the Houston Ship Channel and was taken from my backyard. I like to sit outside and slap mosquitos while watching countless supertankers, barges and cargo ships of every shape and size carry all sorts of deadly toxins to and fro. It's really beautiful at times.....just don't eat the three eyed fish....

    ¯`·.¸¸ .·´¯`· .¸>÷÷(((°>

    `·.¸¸..· ´¯`·.¸ ¸.·´¯` ·.¸>÷÷(((°>

    .·´¯`· .¸>÷÷(((°>

    LMAOSHMSFOAIDMT

  5. #5
    Join Date
    Jul 2011
    Location
    Columbus, Ohio
    Posts
    136
    Post Likes
    Check total static. Suction side negative pressure and compare to air balance report befour speeding up the fan. Return air grills may be dirty evap coil dirty stuff like that.

  6. #6
    Join Date
    Dec 2005
    Location
    Vancouver BC
    Posts
    126
    Post Likes
    Ever since Carrier got the great idea of putting oversized ceramic fiber gaskets on their combustion blower housings I have been dealing with the effects of fouled fan wheels contributing to premature heat exchanger failure. If you put your hand in front of the combustion blower outlet before and after cleaning the wheel you will notice a huge difference in airflow. I would imagine that this translates to larger blowers as well. York had the same issue but they thought to put in a pressure switch rather than going with the centrifugal for air proving.
    ___________________________________________
    These Are The Good Old Days

  7. #7
    Join Date
    Jan 2008
    Location
    Lake Worth, FL
    Posts
    111
    Post Likes
    I've cleaned many a blower wheel (light commercial rooftop) and have had substantial improvement in airflow and comfort.

  8. #8
    Join Date
    Sep 2009
    Location
    PLATTSBURGH, NY 12901
    Posts
    42
    Post Likes
    I once had a system that the blower wheel was full of "crud" and had to go back for frozen up evap. coils. Checked the airflow and it seemed ok. After two service calls an answer surely had to be found. Removed the blower, cleaned the wheel and we have not had a problem since!! Note: this only happened after the unit was replaced with a new R410a split system.
    Last edited by marsmech; 09-13-2011 at 07:03 AM. Reason: Forgot information

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •