+ Reply to Thread
Results 1 to 16 of 16
Thread: Should we abandon our fireplace?
    Aug 2011
    Kingston, Ontario
    We have a 60's house. It has a heatilator type fireplace built around a metal firebox. The air passages appear to be built into the brickwork - there is one low level duct and two high level. I have attached some pics - maybe someone could identify it (no nameplate visible). The glass doors are a later addition.
    The chimney is built of brick and supported by the fireplace and it's foundation. It is about 22x17 OD and appears to have a clay-tile flue inside (or at least that is what sticks out the top).
    Problems we have found:
    - Clearance to combustible framing:- at ceiling level, there is one 2x4 that is hard up against brickwork. A ceiling rafter on one side is 3/4" away and on other side varies from 1-2.5" clearance. Other side has nothing at present. These pieces are not easy to remove and even if possible work would be costly.
    - I found a piece of light gauge steel lying in hearth as well as some sort of a bracket with 4 screws. They can be seen in the second picture. It clearly rusted off. Anyone have any idea what that might be?
    What should we do?
    - We no longer build big fires in the fireplace. At most a couple of those fireplace logs when visitors come and over holidays. I doubt the brickwork even gets warm from one of those, so one option is to just carry on doing that.
    - Abandon fireplace and install a propane insert or just logs? (we don't have natural gas piped in). We would likely just use this as we use the existing logs - just for special occasions. Or we could think of the installation as backup heat if we lose power (we have baseboards/heatpump)
    Questions:
    - If there is an air gap between the brick chomney and the flue, does the 2" clearance requirement still apply?
    - If we install a gas insert or logs, is the existing chimney still used? Or is a separate vent pipe installed?
    - If a separate vent is installed, is the existing chimney sealed to stop heat losses?
    Sep 2011
    Southern Ontario, Can
    Hmm
    In 1975/76? we installed a Heatilator Fireplace at my Dad's. It was a double walled steal heat exchanger with vents top and bottom allowing for convection heat flow. My father hated opening the flue to start a fire as he felt it sucked the heat from the rest of the house, lol. The bricking was just a facade around the heat exchanger. The liner was a regular clay flue liner. I can't remember exactly how it attached to the liner. I would think you would be into some extensive brick work to remove it. The only thing dad thought that would help with the efficiency was a tight fitting glass front that he could not get to work as his bricking had a ledge. I was 19 when me and the brother in-law did the install (I mixed the mortar he was the chimney guy) and though it looked great it was a bust.
    Aug 2011
    Ontario
    Why don't you get a w.e.t. certified pro to give you a assessment? By the book it is not likely legal to use. A propane insert in Ontario requires 2 3" liners run down your chimney to unit. 1 for exhaust and 1 for intake air. All would be good with insert. Wood burning is a whole new book of rules. Insurance will want you to have it wet certified for wood but no questions asked when gas insert installed as long as it meets manufacture specs.
    Hope this helps.
    Aug 2011
    Kingston, Ontario
    Quote Originally Posted by talktowags View Post
    Hope this helps.
    It DOES help - Thanks!
    We are not happy having a chimney with clearances that don't meet code even if we don't use it, except with those food store logs.
    Plan will likely be to instal a gas insert. But that might have to wait until our current heatpump/insulation/airleakage upgrade is complete (and paid for!)
    Air Leakage is a big concern at present. When they run those 3" ducts up through the existing chimney, do they seal around them so there is no air leakage from the room to the chimney?
    Aug 2011
    Ontario
    You can seal around the unit where it meets the brick, not a problem. Make sure they follow manufactures instructions and include it in quote.
    S.E. Pa
    Cool
    You should start with an inspection by a WETT certified pro. You can pack insulation around the two liners but it never seals 100%.
    Any gaps between the steel fireplace form and the surrounding masonry must be sealed even with an insert regardless of fuel type. Note that any insert is not recognized as a repair item.
    Sep 2011
    Quote Originally Posted by Freeagent View Post
    Plan will likely be to install a gas insert. But that might have to wait until our current heatpump/insulation/airleakage upgrade is complete (and paid for!)
    As an Engineer you know that specific information for particular devices must be looked up and the ability to find this material is part and parcel of your job. This is no different here manufacturers supply detailed instructions for correct installation and it is mandated that the installer read these instructions. This does not preclude you as a customer form obtaining and reading the same information. We live in an age were this information is a click away. If you know the model go to the manufacturer's site and lock up the tech sheets, this applies from toilets to fireplaces. Here is and example:http://www.napoleonfireplaces.com/Te...ls/BGD33NR.pdf
    RTFM as troubletime likes to say, lol.
    May 2011
    Colorado Springs
    Fireplaces are a luxury item that do not provide anything near the COP as your standard gas furnace AHU. Seal it up and you'll save a fortune on wasted energy going out the flue.
    However, a stove that radiates heat all around it, is a luxury item that actually delivers heat generating a COP comparable to a gas furnace.
    Aug 2011
    Kingston, Ontario
    Quote Originally Posted by bironacad View Post
    One thing I learned as a design engineer, was to ask the practical guys who maintained and operated equipment before choosing anything. The manual thing come later
    There is a lot of terminology around these fireplaces and I am just picking it up. Especially when it comes to retrofitting an insert.
    Quote Originally Posted by hearthman
    We have two problems - lack of clearance from combustible at ceiling penetration and rust up above damper including one or two parts that fell down (see pic). Fixing the clearance problems would require some demolition of interior walls and will not be an easy or inexpensive fix. Changing a rusty firebox, even worse, I would imagine.
    I have set up an appointment for an inspection, but it will probably be a waste of money because it seems clear that our FP/chimney is not safe as it is. I may instead, just have them clean the chimney in preparation for a future conversion to gas and just stop using the FP for now.
    Quote Originally Posted by lafittejdubb
    You are right! We are currently removing our Jotul woodstove in another room - It did provide a lot of heat, but we are past the wood chopping stage . If we put in a gas insert, it will just be for cosmetics and backup for our BB/Heatpump if the power goes off.
    S.E. Pa
    Cool poor comparison
    Quote Originally Posted by lafittejdubb View Post
    Not sure how you would apply COP to a hearth product that is not a heat pump. There are many reasons to buy a hearth product other than pure heating efficiency alone. Even when you address efficiency, there are many ways to look at that.
    You can compare AFUE's where a typical gas direct vent approaches your typical fan assisted furnace. You can look at combustion efficiency and know that the fireplace will be lower but keep in mind, it is a luminous flame appliance so by definition, it will be lower. Then you have the less tangible aspects. For instance, many clients report actual fuel savings with a gas DV insert because they use it as a zone heater for the bulk of the day thus burning less fuel overall. Now where is your COP?
    Hearth appliances are also built and installed for aesthetics. Look in those home decor magazines and show me a pic of a family gathered around the furnace or boiler. The hearth is a gathering place for the family and friends. There is valiue to that. They look nice, which also holds value. They can function as a backup heat source so you can remain in your home during a winter storm and be comfortable while your main furnace sits cold. Something no furnace has been able to do is provide that sense of security and joy that comes from sitting around a fireplace or stove.
    Just so you understand, direct vent gas inserts are blocked off so you don't lose a ton of heat up the chimney, suffer from cold smelly downdrafts or pollute the home with CO, aldehydes and NOx the way a backdrafting furnace can. Since it does not draw indoor air, it does not cause thermostats to cycle as cold air infiltrates into the home the way a typical 80% furnace does or a CAT IV furnace with an exhaust pipe only does.
    Which costs more in energy: a sealed direct vent gas fireplace insert properly installed and operated as a zone or supplemental heater or a gas furnace improperly set up, not tuned with leaky ductwork, a clogged filter and a Hg thermostat located in a return bay or too close to the front door?
    lafittejdubb but I disagree with your broad characterization. It is not an apples to apples comparison.
    Aug 2011
    Kingston, Ontario
    I did find a good reference to gas fired fireplaces that has helped in getting a general understanding of what we should be looking at:
    http://dsp-psd.pwgsc.gc.ca/Collectio...23-9-2003E.pdf
    We are spending $20k on our heat pump/energy upgrades this year, so the FP will have to wait. Meantime it will not be used!
    Sep 2011
    Practical guy here, lol, I have found that discussion forums are and excellent way to get a broad overview of a topic. I recently purchased a tractor for the farm and found the shared experience of a discussion forum immensely helpful. One thing that was suggested is that I load a free download for spell checking my posts, lol, http://www.iespell.com/ I still have challenges with my posts at times but the speel check helps.
    May 2011
    Colorado Springs
    Red face My apologies
    Quote Originally Posted by hearthman View Post
    HEARTHMAN, I apologize for hitting a nerve with you! I should have been more careful with my words considering your response to my post.
  14. #14
    S.E. Pa
    Thumbs up everyone has their viewpoint
    No apologies needed. We all have our frame of reference. This is an HVAC site that also discusses fireplaces. You go on a Hearth related site or home inspectors and I'm sure you'll see things that perturb you. Just how it is. However, if we're open and objective, we all learn. I never thought of applying COP to hearth products before but the concept does bring another dimension into choices.
    Thanks for participating and please don't stop!
  15. #15
    May 2011
    Colorado Springs
    Thanks Hearthman!
  16. #16
    Aug 2011
    Kingston, Ontario
    Hope this helps.
    This is the route we are going to go. I just can't see a way to increase the spacing from brick chimney to combustible framing and internal parts of liner (probably off damper) have rusted. Don't think chimney would pass even although in itself it is very sound.
    We will have chimney cleaned next week. After that, a sealed cap will be installed to eliminate draft until we a propane fired insert installed.
    I am thinking we should buy a basic unit to keep costs down. FP will be used for cosmetic ambience at Christmas Thanksgiving etc. Only in case of power outage will we want to use unit for heating (because propane costs us more than electricity) so efficiency not that important.
    Any suggestions? I know we can't discuss pricing, but I would be interested in a lo-med-high rating of suitable units.
+ Reply to Thread