Thread: Beverage Air Cap Tube Problems

  1. #1
    Join Date
    Sep 2011
    Location
    Augusta, ME
    Posts
    135
    Post Likes

    Beverage Air Cap Tube Problems

    I am working on a 4ft. long Beverage Air, make table refrigerator and I am having some issues with finding correct cap tube size and length. I am going to be running hot shot due to cap tube plugging issues in the past. The compressor is a tecumseh AZA0395YXA. The supco guide said 92" of 0.028ID cap tube and this starved the evap badly. Any input would be appreciated.

  2. #2
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,309
    Post Likes
    Forgive me for stating the obvious, but did you call bev-air? Get on the phone with one of their engineers and they can give you the best advice. After all, it IS their equipment.
    Every customer you take for granted today will be someone else's tomorrow.

  3. #3
    Join Date
    Sep 2009
    Location
    PLATTSBURGH, NY 12901
    Posts
    42
    Post Likes

    Wink

    Have you also thought of changing it to a TXV. I have done this now on four reach ins. Every customer has mentioned the difference in operation, runtime, and overall experience with the cooler. Call the manufacturer get all the specs. Total btu's needed, btu's for the compressor at the temperature you are cooling to, and a recommend valve size. They may not recommend a valve as it is out of spec but I am out of experience believe this is the best avenue if you do not want continous service calls! Good luck!!!

  4. #4
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    Quote Originally Posted by sgagne199 View Post
    I am working on a 4ft. long Beverage Air, make table refrigerator and I am having some issues with finding correct cap tube size and length. I am going to be running hot shot due to cap tube plugging issues in the past. The compressor is a tecumseh AZA0395YXA. The supco guide said 92" of 0.028ID cap tube and this starved the evap badly. Any input would be appreciated.
    The best capillary tube sizing calculator available would have picked a 0.028" cap at 51" length at a 20F evap, 120F condensing, and 36" heat exchange. http://boxload.tecumseh.com/

    Dump the Supco and J/B charts. You are throwing rocks at the broad side of a barn.

    The Beverage Air folks will have a better idea which capillary tube works best with their equipment.
    If we have data, let’s look at data. If all we have are opinions, let’s go with mine. – Jim Barksdale, former Netscape CEO

  5. #5
    Join Date
    Nov 2009
    Posts
    1
    Post Likes
    Just changed one last week on a single door Ref....It was .049 and 100" long ...Call Bev Air with model # and they well tell you what to run ...

  6. #6
    Join Date
    Sep 2011
    Location
    Augusta, ME
    Posts
    135
    Post Likes
    Thread Starter
    I would consider converting to a txv but customer would never go for that no matter what benefits it may entitle. I called bev air and they said 84in of 0.036 ID cap tube.

  7. #7
    Join Date
    Sep 2011
    Location
    Augusta, ME
    Posts
    135
    Post Likes
    Thread Starter
    and yeah after changing a few cap tubes I have noticed not to go by Supco and J/B charts haha they arent very accurate at all in my experience

  8. #8
    Join Date
    Dec 2007
    Location
    Chandler AZ
    Posts
    177
    Post Likes
    make sure you charge compressor oil so you don't have to do it twice . I learned that the hard way .

  9. #9
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    When I put in those numbers in here http://hvac-talk.com/vbb/showthread.php?t=751621 I got 26.44" of .028 from the .036 length



    Guess the best bet is to call the manufacturer*




    *(willing to bet Andys picks a better cap on some other brands though)




    I believe your web apps will push me over the fence for a smart phone.
    Thanks Andy for putting together some great info there for us
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  10. #10
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    [QUOTE=itsiceman;11293282]

    itsiceman,
    I like your avitar its kinda like { winning the lottery and dying the next day }


    Oh and i looked at a Victory 3 door freezer yesterday. It was marked that someone replaced the cap tubes. 2 cap tubes about 3' long smaller then original So i call Victory and tech says it takes .042 @ 7'-6" long. So i look at Supco chart and it says .031 @ 39" long.

  11. #11
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    The Supco and J/B charts only guesstimate at the design operating conditions of the equipment. Sizing capillary tubes on the basis of compressor horsepower vs low, medium, and high temp application is attempting to hit the broad side of a barn with a heavy rock at 100 feet.

    OEM tech support will know the design conditions of their equipment, and the appropriate capillary tube sizing.

    If this information isn't available, I have the next best solution.
    If we have data, let’s look at data. If all we have are opinions, let’s go with mine. – Jim Barksdale, former Netscape CEO

  12. #12
    Join Date
    Dec 2000
    Location
    phoenix, arizona
    Posts
    1,149
    Post Likes
    Quote Originally Posted by Andy Schoen View Post
    The best capillary tube sizing calculator available would have picked a 0.028" cap at 51" length at a 20F evap, 120F condensing, and 36" heat exchange. http://boxload.tecumseh.com/

    Dump the Supco and J/B charts. You are throwing rocks at the broad side of a barn.

    The Beverage Air folks will have a better idea which capillary tube works best with their equipment.
    Hi Andy, Is it possible to modify the cap tube program (see attachment)?.
    I would be very useful if a particular compressor is already in the system, and I wanted to replace the restricted cap tube.

    Edit; I am un-able to up to load attachment. my question is; would it be possible to modify the program, so I input the compressor model # instead of system capacity? Existing compressor is already there, I want to know replacement size tubing based on existing compressor.
    Thank
    Dan Wong
    Last edited by dan wong; 09-29-2011 at 04:24 AM. Reason: unable to up load attachment
    Decide what you want, decide what you are willing to exchange for it. Establish your priorities and go to work." H.L. Hunt

    "In order that people may be happy in their work, these three things are needed: They must be fit for it. They must not do too much of it. And they must have a sense of success in it." John uskin

  13. #13
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    Quote Originally Posted by dan wong View Post
    would it be possible to modify the program, so I input the compressor model # instead of system capacity? Existing compressor is already there, I want to know replacement size tubing based on existing compressor.
    Thank
    Dan Wong
    Yes, this would be simple to do. I probably would want to figure out a way to give the user the option to enter compressor model number or system capacity. I would still need to know the evap and condensing temperatures in either case.
    If we have data, let’s look at data. If all we have are opinions, let’s go with mine. – Jim Barksdale, former Netscape CEO

  14. #14
    Join Date
    Dec 2000
    Location
    phoenix, arizona
    Posts
    1,149
    Post Likes
    Quote Originally Posted by Andy Schoen View Post
    Yes, this would be simple to do. I probably would want to figure out a way to give the user the option to enter compressor model number or system capacity. I would still need to know the evap and condensing temperatures in either case.
    Hi Andy, Any idea when you may have it done?

    Something else came to my mind; Many manufacture use Hi temp compressor for medium temp application, example; I often see AE4440yxa ( a hi temp compressor, rated at +45F) used on medium temp equipment (evaporator is +20F. Cabinet temp is normally kept at +35 – 40F).

    If you can set the program to accept several different input perimeters like following;
    (in addition to what you already have)


    Compressor Model # _____________________
    BTU@rating point. _________@ ______ (C/F)


    Desire out;

    Desire evaporator temp ______________(C/F)
    ( normally +20F for medium temp reach in)

    Size of a Cape tube recommended (3 equaling choices);

    Id _______inches, length _______________ inches
    Id _______inches, length _______________inches
    Id _______inches, Length _______________ inches
    Decide what you want, decide what you are willing to exchange for it. Establish your priorities and go to work." H.L. Hunt

    "In order that people may be happy in their work, these three things are needed: They must be fit for it. They must not do too much of it. And they must have a sense of success in it." John uskin

  15. #15
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    You might find my compressor performance app useful: http://boxload.tecumseh.com/

    I'm currently working on my refrigerant line sizing app. I should have it up within the next week. I'll take a look at the capillary tube sizing program next.
    If we have data, let’s look at data. If all we have are opinions, let’s go with mine. – Jim Barksdale, former Netscape CEO

  16. #16
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Wow Andy great info and calculators/analyzers Keeps getting better
    Thanks for taking the time to get that going.
    Is there a way onto that page through the main web sight?
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  17. #17
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    Quote Originally Posted by itsiceman View Post
    Is there a way onto that page through the main web sight?
    Not at the moment. I've been given this "sandbox" site to play around in and develop useful apps for our main web site.
    If we have data, let’s look at data. If all we have are opinions, let’s go with mine. – Jim Barksdale, former Netscape CEO

  18. #18
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    I used the cap program today on a habitual cap restricting model and really liked the way it ran.
    Big Improvement over factory size IMO
    Thank You Very Much Andy

    FWIW original size was 10' of .046 I used 6' of .052
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  19. #19
    Join Date
    Sep 2011
    Location
    South Florida - SC
    Posts
    17
    Post Likes
    I know cap tube diameter Is critical as a fixed orifice metering device, but the length is not! Note there may me a extra coil of 4 ft rolled up there & there may not be. Change the cap tube. Now throw the minimum charge in there per the tag inside the box. By the way True & 134a cap tubes are notorious for oil separation. Ok, now you need to take your super heat readings in 2 places. At the suction before the compressor , up to 20 is ok, some Coprland says 30 is ok, but Tecumseh, 20 THERE is ok. Now take super heat reading at the evap after the cap tube goes into the evap. Should be 8 to 14. Also IF you had bad separation and you didn't flush it e flush? Then no matter what you do, you'll come up short, this all has to be done right... Right down to sucking the old oil out to replacing it. On 134a, when the condenser overhears , that POE oil ( is
    Acid based) separated and a waxy substance clogged your cap in the first place! Another thing could have been that the other 1/2 of the seperation could have ate through the cap tube. So if u didn't change the oil & simply replaced the cap tube, the new one could be partially clogged w wax and it's fooling u to think it's the charge! Yes like an ice machine, charge IS CRITICAL. also, are you primarily AC over refrigeration? Cause if u r and you dud superheat only at the compressor, you might be overcharged w a flooded evaporator. What's your amp probe say? If it's high to rated. Then she's over charged. I'm telling u all this cause you can't b a DIY in my opinion. Was the condenser clogged or overheated when u arrived? I need to know more, tell me more! I'll help u out.

  20. #20
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,659
    Post Likes
    Quote Originally Posted by beeninyourshoes View Post
    I know cap tube diameter Is critical as a fixed orifice metering device, but the length is not!
    You need some big time remedial education.

    Quote Originally Posted by beeninyourshoes View Post
    II'm telling u all this cause you can't b a DIY in my opinion. Was the condenser clogged or overheated when u arrived? I need to know more, tell me more! I'll help u out.
    And you're likely to remain a guest at this site for a very long time....
    If we have data, let’s look at data. If all we have are opinions, let’s go with mine. – Jim Barksdale, former Netscape CEO

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •