    working on mamouth unit putting in tandem scroll replacements after a ground out. put in first set in one unit no problems. installed another set in another unit first compresser comes up no problem start the secound hear grinding noise from both first locks up in less than a minute. got new one on warranty replaced number one. number two ran by itself all week just fine. start up the warranty one starts fine. start number 2 same as last time but this time notice oil glass on number one goes empty, 2 fills up 1 starts grinding and bam! tries to lock up. return tomorrow to start back on it. looking for anybody run into something similar?

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,674
    Post Likes
    Alan,

    You should apply for professional membership.

    You mentioned that these are replacement compressors.

    Did you install the correct fittings when they were piped in?

  3. #3
    Join Date
    Aug 2011
    Location
    Los Angeles, CA
    Posts
    34
    Post Likes
    Is there an oil equalizing line between the two? Is it plugged?

  4. #4
    Join Date
    Mar 2003
    Posts
    7,381
    Post Likes
    more importantly, did you fix the cause of the failure? ot at least know what it is?

  5. #5
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    184
    Post Likes
    Trane had a problem with tandem scrolls loosing oil in the 1st compressor. They installed a washer type orifice in the downstream compressor to force more oil to return into the first compressor. You need to contact Mammoth and find out if they are doing the same thing. If they are you will need to make sure the orifice is in place. Can you post the compressor model no.?