  1. #1
    Join Date
    Apr 2005
    Location
    Virginia
    Posts
    176
    Post Likes
    Went to a call today that the homeowners were complaining about the air pulsating out of the vent. Which is noticiable but not that bad. Real picky homeowners. The fisrt thing i did was place the fan setting on low and left the door of to see if it was starving for air but the unit still pulsated. I did notice a slight drop in power going to unit. I mean real slight drop, which would be .5 volts at most. This particular system is a 2 ton york. The duct system is fairly simply with only 7 supplies coming of 10 inch round duct off of each side of supply plenum. 4 supplies off of one side and 3 off of other. 6 inch flex for each supply. I know, I know do a manual d for duct design. But should the air still pulsate on low speed which according to papers with airhandler says at a .1 static pressure cfm is 650. Each 6" round is around 100 cfm but 6 inch flex duct only producing 80 cfm. If you take the 7 supplies and mutliply time 80 you have 560 cfm which still seems short. but enough to cause the pulsating?

  2. #2
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    24,816
    Post Likes
    Could be a weak motor winding.

  3. #3
    Join Date
    Apr 2005
    Location
    Virginia
    Posts
    176
    Post Likes
    Thread Starter
    I should have mentioned that I did replace motor and capacitor because I to thought that something was wrong with the motor.

  4. #4
    Join Date
    Dec 2003
    Location
    Location!, Location!
    Posts
    930
    Post Likes
    any chance the flex is sagging or too long and moving with the positive pressure?

  5. #5
    Join Date
    Jan 2003
    Location
    Kansas City
    Posts
    1,526
    Post Likes
    I can't imagine a psc blower motor changing speeds in a way that would cause an airflow pulsation. I would be looking for things like water in the flex ducts where they sag. Could you have an electric bypass damper that is driving or a barometric damper that is bouncing?

  6. #6
    Join Date
    Apr 2005
    Location
    Virginia
    Posts
    176
    Post Likes
    Thread Starter
    you can hear the pulsation in in just about all the supplies. Not terrible but it is noticable

  7. #7
    Join Date
    Oct 2004
    Location
    Tyler, TX
    Posts
    3,400
    Post Likes
    Is the return flex?
    RSES Certificate Member Specialist

    Southwest Regional Association of RSES Secretary, 2017

  8. #8
    Join Date
    Apr 2005
    Location
    Virginia
    Posts
    176
    Post Likes
    Thread Starter
    the returns are flex. Two returns which are a 12 inch and the other a 10 inch. This unit is in the attic and there seems to be no sags in flex.

  9. #9
    Join Date
    Jul 2004
    Location
    midwest
    Posts
    2,869
    Post Likes
    You answered my question while I was typing.

    [Edited by trane on 12-14-2005 at 06:10 PM]

  10. #10
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    24,816
    Post Likes
    If you had the blower door off and it still did the same thing, then I doubt its a return problem. You say you replaced the motor and capacitor and still have the same problem,,hmmmm..(scratching my head). It has to be a voltage problem then. Are you sure you did not replace it with a 230vac motor? Check the rating plate. Maybe the distributor gave you the wrong motor.

    Then again a 230 motor would be moving alot slower.

  11. #11
    Join Date
    Jul 2004
    Location
    midwest
    Posts
    2,869
    Post Likes
    If my memory is right, we had a York air handler doing this and had to add more static to the return.

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Remove one of the 10" flex trunks and see if it still does it.

    Could there be water laying in the flex from this summer.

  13. #13
    Join Date
    Apr 2005
    Location
    Virginia
    Posts
    176
    Post Likes
    Thread Starter
    the two 10 inch round supply ducts are metal duct with 6 inch flex tap offs to each vent. a total of probably 30- 35 feet of main trunk line 10 inch all the way with 2 45's on one side to offset because of tray cieling. 15 feet on one side and maybe 15-20 feet on other side of main trunk line. on both sides of trunk line the last takeoff seems to be a good foot from each end

  14. #14
    Join Date
    Jun 2000
    Location
    WYO
    Posts
    2,187
    Post Likes
    Ill bet on the coils plugged up

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •