    no superheat, no subcooling

    Here is the situation... Design pressures are 150/300psi with 12 degree subcooling...

    Actual conditions are 92Psi liquid at a temperature of 69F. High pressure side is at around 220Psi and about 12F BELOW saturation temperature. Cooling isn't really doing much indoors and runs constantly.

    Is the compressor on the way out or is there a charge issue here. Forgive me as I am fairly new to the service industry.

    Thanks in advance guys

  2. #2
    Join Date
    May 2009
    Location
    Jacksonville FL
    Posts
    4,581
    Post Likes
    you have 14 deg superheat on r22 at that pressure and temp. The 92 is the suction not the liquid. The liquid (or high pressure or head pressure) temp should read below the saturation temp (it does SUBCOOL the refrigerant after all).

    Your suction pressure is kinda high. This could be caused by hot temperature inside or high airflow. Is this a txv system?

  3. #3
    Join Date
    Jul 2010
    Posts
    53
    Post Likes
    Thread Starter
    R22 is the refrigerant

  4. #4
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    Quote Originally Posted by 02powerstroke View Post
    Here is the situation... Design pressures are 150/300psi with 12 degree subcooling...

    Actual conditions are 92Psi liquid at a temperature of 69F. High pressure side is at around 220Psi and about 12F BELOW saturation temperature. Cooling isn't really doing much indoors and runs constantly.

    Is the compressor on the way out or is there a charge issue here. Forgive me as I am fairly new to the service industry.

    Thanks in advance guys
    I am kind of lost in your post...

    Fill this out for me:

    Refrigerant type (22,410,134)?
    Type of system (split, package, chiller)?
    Metering device (TXV, orifice, cap tube)?
    Suction pressure?
    Suction line temp?
    Liquid line pressure?
    Liquid line temp?
    Return air temp?
    Temp drop across the evap coil?

    This will help us get started.
    UA LU189

  5. #5
    Join Date
    Jul 2010
    Posts
    53
    Post Likes
    Thread Starter
    I'll get to a laptop quick and fill that out..

  6. #6
    Join Date
    May 2009
    Location
    Jacksonville FL
    Posts
    4,581
    Post Likes
    What is your coil temp difference? Do you have duct leakage to have high suction like that?

  7. #7
    Join Date
    Jul 2010
    Posts
    53
    Post Likes
    Thread Starter
    Quote Originally Posted by zw17 View Post
    I am kind of lost in your post...

    Fill this out for me:

    Refrigerant type (22,410,134)? R22
    Type of system (split, package, chiller)? Split
    Metering device (TXV, orifice, cap tube)? TXV
    Suction pressure? 92 psi
    Suction line temp? 69F
    Liquid line pressure? ~220 psi
    Liquid line temp? 108F
    Return air temp? Didn't measure this, however the thermostat is set to 79F.
    Temp drop across the evap coil? Supply air temperature is 67F.
    This will help us get started.
    I edited the quote to include the requested information

    Also, if my suction line pressure is 92psi and my saturation temp is about 57F. If my suction line temperature is 69F, doesn't that mean I have no subcooling?

  8. #8
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by 02powerstroke View Post
    I edited the quote to include the requested information

    Also, if my suction line pressure is 92psi and my saturation temp is about 57F. If my suction line temperature is 69F, doesn't that mean I have no subcooling?
    no that means you have 12* superheat. Line temp - Sat temp = superheat for suction and subcool for liquid.

    I really reccomend you learn what this is, the superheat / subcool as you can not diagnose a refrigeration issue w/o this. It's kinda like your blood pressure
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  9. #9
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    You have 14*F superheat
    You have 0*F subcooling

    That 0*F subcooling tells me you are way undercharged.
    UA LU189

  10. #10
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,723
    Post Likes
    Quote Originally Posted by 02powerstroke View Post
    if my suction line pressure is 92psi and my saturation temp is about 57F. If my suction line temperature is 69F, doesn't that mean I have no subcooling?
    The suction line is superheated gas returning to the comp from the indoor coil. If sat. temp is 57 and the gas is 69, you have 12F of superheat.

  11. #11
    Join Date
    May 2004
    Location
    Frederick, MD
    Posts
    1,058
    Post Likes

    Something

    is not adding up here. How can you have 12-14 degree superheat and no subcooling? The TXV will be wide open with no liquid to it, only vapor. S/H should be much higher.

  12. #12
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,723
    Post Likes

    Smile

    Quote Originally Posted by gregp View Post
    is not adding up here. How can you have 12-14 degree superheat and no subcooling? The TXV will be wide open with no liquid to it, only vapor. S/H should be much higher.
    Saturated refrigerant can be any combination of liquid and vapor, as long as both are present.

  13. #13
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    02, have you tried adding gas? I would start by adding until you see you liquid line temp start to drop a bit. No more than 2-3lbs though.

    If you don't have the manufactures recommendation on target subcooling I would shoot for 10*F to start. Check your temp drop and superheat and report back to us.
    UA LU189

  14. #14
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Yep..

    Add some gas and you will settle down.

    Probably even bring your suction pressure down, too.

    Bonus points for the OP if he can explain why suction will drop...



  15. #15
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by Southern Mech View Post
    I really reccomend you learn what this is, the superheat / subcool as you can not diagnose a refrigeration issue w/o this. It's kinda like your blood pressure
    I could not agree with this post more.

    You NEED to understand subcooling and superheat before you can consider yourself competent in this field.



  16. #16
    Join Date
    Jul 2010
    Posts
    53
    Post Likes
    Thread Starter
    sorry for the confusion.. yes that is correct, I have about 12F of superheat and a couple degrees of subcooling, at best.. I had to run to grab some parts for another job, but will re-measure in a little while... as for now, I didn't want to add gas just yet.. wanted to be sure

  17. #17
    Join Date
    Jul 2010
    Posts
    53
    Post Likes
    Thread Starter
    I keep mixing my lines up, and it came out in the form of subcooling/superheat confusion... yes, I have about 12F of superheat coming into the compressor via the suction line... the liquid line has nearly no subcooling to it.. I am going to re-attach the gauges in a bit, when I return to the site, to be sure of my numbers I quoted above.

  18. #18
    Join Date
    Jun 2003
    Location
    Gulf Coast
    Posts
    281
    Post Likes
    Quote Originally Posted by 02powerstroke View Post
    Here is the situation... Design pressures are 150/300psi with 12 degree subcooling...

    Actual conditions are 92Psi liquid at a temperature of 69F. High pressure side is at around 220Psi and about 12F BELOW saturation temperature. Cooling isn't really doing much indoors and runs constantly.

    Is the compressor on the way out or is there a charge issue here. Forgive me as I am fairly new to the service industry.

    Thanks in advance guys
    Why is the design pressures so high 150PSI suction on R22. Where did you get the design pressures are you sure thats not the testing pressure?

  19. #19
    Join Date
    Jul 2010
    Posts
    53
    Post Likes
    Thread Starter
    Quote Originally Posted by waltervan View Post
    Why is the design pressures so high 150PSI suction on R22. Where did you get the design pressures are you sure thats not the testing pressure?
    this was from the manufacturer's information... suction pressure will drop on the suction side when you add refrigerant since you have more refrigerant to absorb heat... since there is more refrigerant you will have more refrigerant to absorb the energy and will result in less liquid refrigerant turning into a gas, or vaporizing

    what do I get?

  20. #20
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by 02powerstroke View Post
    this was from the manufacturer's information... suction pressure will drop on the suction side when you add refrigerant since you have more refrigerant to absorb heat... since there is more refrigerant you will have more refrigerant to absorb the energy and will result in less liquid refrigerant turning into a gas, or vaporizing

    what do I get?
    You get to try again......




+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •