    mfd capacitor

    hi i would like to know if i have a good run capacitor but dont understand how to do the math on the mfd it is a 7.5 cap and it reads 7.02 is this a good cap and tolerance is 6% how do you calculate the math to tell its good or bad
    Thanks

  2. #2
    Join Date
    Jun 2010
    Location
    North Fl
    Posts
    154
    Its so close... A new capacitor is about $ just change it
    Last edited by beenthere; 09-10-2011 at 06:33 AM. Reason: price
    HOW MUCH DID YOU SAY???

  3. #3
    Join Date
    Jun 2011
    Posts
    229
    Most people I talk to say they go as far as 10%. I personally go off whatever the cap says. Id recommend replacing it.

  4. #4
    Join Date
    May 2011
    Posts
    17

    cap

    Quote Originally Posted by Redwood650 View Post
    Most people I talk to say they go as far as 10%. I personally go off whatever the cap says. Id recommend replacing it.
    hey thanks but i still want to know how you come to the -6 +6 do you take 7.5 x .06 = 0.45 what is 6%

  5. #5
    Join Date
    May 2011
    Posts
    17

    cap

    hey thanks but i still want to know how you come to the -6 +6 do you take 7.5 x .06 = 0.45 what is 6%
    i want someone to do the math for me here so i can see the steps

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,097
    7.5X.06=.45
    7.5-.45=7.05
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Mar 2007
    Location
    north carolina
    Posts
    32
    7.5x.94=7.05

  8. #8
    Join Date
    Dec 2010
    Location
    Down by the river
    Posts
    1,664
    Quote Originally Posted by deon View Post
    7.5x.94=7.05
    what's the .94? never seen this
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  9. #9
    Join Date
    May 2011
    Posts
    17
    Quote Originally Posted by Southern Mech View Post
    what's the .94? never seen this
    sorry 7.5 x .06 = 0.45

  10. #10
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    5,591
    Quote Originally Posted by Southern Mech View Post
    what's the .94? never seen this
    .94 = 94% or 6% less than 100%.

    So if the capacitor is less than 94%, it is outside the 6% tolerance.
    Instead of learning the tricks of the trade, learn the trade.

  11. #11
    Join Date
    Jul 2005
    Posts
    5,571
    Quote Originally Posted by Southern Mech View Post
    what's the .94? never seen this
    It's 1 - 0.06.

    A little algebra:

    7.5 x 0.06 = 0.45
    7.5 - 0.45 = 7.05

    Substitute the left side of eq.1 for the 0.45 in eq.2. You get

    7.5 - 7.5 x 0.06 = 7.05

    factor out the 7.5 to get

    7.5 (1- 0.06) = 7.05

    or

    7.5 x 0.94 = 7.05

  12. #12
    Join Date
    Jul 2005
    Posts
    5,571
    Quote Originally Posted by hvacrmedic View Post
    It's 1 - 0.06.

    A little algebra:

    7.5 x 0.06 = 0.45
    7.5 - 0.45 = 7.05

    Substitute the left side of eq.1 for the 0.45 in eq.2. You get

    7.5 - 7.5 x 0.06 = 7.05

    factor out the 7.5 to get

    7.5 (1- 0.06) = 7.05

    or

    7.5 x 0.94 = 7.05
    Or IOW 94% of 7.5.

  13. #13
    Join Date
    May 2011
    Posts
    17

    hvacmedic

    Excellant thats what i wanted to know thanks man and all you other people i appreciate it i never knew this


    Quote Originally Posted by hvacrmedic View Post
    It's 1 - 0.06.

    A little algebra:

    7.5 x 0.06 = 0.45
    7.5 - 0.45 = 7.05

    Substitute the left side of eq.1 for the 0.45 in eq.2. You get

    7.5 - 7.5 x 0.06 = 7.05

    factor out the 7.5 to get

    7.5 (1- 0.06) = 7.05

    or

    7.5 x 0.94 = 7.05

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event