    The theory of charging an R22 system without a TXV

    It is my understanding that the correct way to charge an R22 system without a TXV is by getting the actual superheat to match the target superheat. It is also my understanding that the target superheat in Fahrenheit is determined by the equation:

    Target superheat = (3 x Indoor Wet bulb temperature – 80 – Outdoor ambient temperature)/2

    And the actually superheat:

    Actually superheat = Suction line temperature – the refrigerant boiling point for the measured suction line pressure.

    I’ve found different sources that claim this is the correct method including the manual for my condensing unit. Nonetheless I have yet to meet an HVAC technician who agrees with this or for that matter even had a web bulb thermometer or digital psychrometer in their possession. The last technician said it was good enough to get around ten degrees of actual superheat no matter what.

    What is the truth?

  2. #2
    Join Date
    Jan 2008
    Posts
    2,028
    The truth is there are many "techs" who can't or won't properly charge a system. It's called "beer can cold". Get the suction line sweating and they're down the road.
    Yes, a fixed orifice system should be charged to target super-heat, plus or minus 3 degrees. TXV system to mnf specs of sub-cool.
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler

  3. #3
    Join Date
    Sep 2009
    Location
    Hampton, GA
    Posts
    571

    Talking

    Ok... Hold steady here comes a barrage of replies... loll

  4. #4
    Join Date
    Dec 2010
    Location
    Down by the river
    Posts
    1,664
    all systems have a target superheat or and subcool. I never come up with some algebraic equasion, I go by what the manufacture suggests. Of course they had to use some equasion to come up with it, but they are engineers and scientists, and I just fix their design flaws.

    all techs must have someway of knowing wetbulb temperature of the area being conditioned.
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  5. #5
    Join Date
    Jun 2011
    Location
    Wake Forest, NC
    Posts
    352
    An ideal charge is done by weight. Charge according to the data plate on the equipment and add .6 oz or R-22 per additional foot of line set beyond 15 feet for a 3/8 X 3/4 line set. On older equipment the factory charge accounted for a 25 foot line set, so check with the manufacturer if it more than about 10 years old.

    When charging by weight isn't the best option (after a leak has been repaired) then charge by superheat for fixed orafice systems and by subcooling for TXV applications. The system should have a charging chart that will give the required superheat or subcooling data for the system and a qualified tech should be able to read and accurately interpret the chart and its data to charge the system properly so long as they have some kind of digital thermometer with a strap on temperature probe and a sling psychrometer or a digital psychrometer.

    It never ceases to amaze me the number of "qualified technicians" who dont know the correct way to charge a system.
    It's not rocket-science...

    It's electromechanical thermodynamic engineering

  6. #6
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    2,916
    Quote Originally Posted by mofotech View Post
    Ok... Hold steady here comes a barrage of replies... loll
    I have a psychrometer and know how to charge to +/- 3 degrees.......

    where have you been finding your "techs"?

    some days 20 degrees of superheat is correct. 2 months ago I had to take 12 lbs out of a system that only held 9 lbs- must have liked really cold beer

  7. #7
    Join Date
    Feb 2010
    Location
    Ontario Canada
    Posts
    1,341
    Yep, Beer can cold, +/_ 3*.........
    Never give up; Never surrender!

  8. #8
    Join Date
    Sep 2009
    Location
    Hampton, GA
    Posts
    571
    What if there is no chart on the condenser or its been ripped off by erosion. What base Superheat and Subcooling one should aimed for? Is having Superheat 12-15 degrees normal? And having 9-12 degrees normal for subcooling?

  9. #9
    Join Date
    Oct 2010
    Location
    SW Michigan, near Battle Creek
    Posts
    921
    if you like english beer beer can cold can be prety close

  10. #10
    Join Date
    Oct 2010
    Location
    SW Michigan, near Battle Creek
    Posts
    921
    the formula for superheat. seems I,m often shooting for 20-30 up here in the north country

  11. #11
    Join Date
    Jun 2011
    Location
    Wake Forest, NC
    Posts
    352
    Quote Originally Posted by mofotech View Post
    What if there is no chart on the condenser or its been ripped off by erosion. What base Superheat and Subcooling one should aimed for? Is having Superheat 12-15 degrees normal? And having 9-12 degrees normal for subcooling?
    Contact the local distributor for said brand and get the # for tech support. Call them with models and serials and they can give you all the information you need (and then some more....)
    It's not rocket-science...

    It's electromechanical thermodynamic engineering

  12. #12
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,675
    Quote Originally Posted by 2old2rock View Post
    The truth is there are many "techs" who can't or won't properly charge a system. It's called "beer can cold". Get the suction line sweating and they're down the road.
    Yes, a fixed orifice system should be charged to target super-heat, plus or minus 3 degrees. TXV system to mnf specs of sub-cool.
    This is the truth and nothing but the truth.


    There is something else that MUST be factored in, but if your techs don't have psychrometers, they aren't checking that, either......

  13. #13
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    7,126
    Quote Originally Posted by sneuberg View Post
    It is my understanding that the correct way to charge an R22 system without a TXV is by getting the actual superheat to match the target superheat. It is also my understanding that the target superheat in Fahrenheit is determined by the equation:

    Target superheat = (3 x Indoor Wet bulb temperature – 80 – Outdoor ambient temperature)/2

    And the actually superheat:

    Actually superheat = Suction line temperature – the refrigerant boiling point for the measured suction line pressure.

    I’ve found different sources that claim this is the correct method including the manual for my condensing unit. Nonetheless I have yet to meet an HVAC technician who agrees with this or for that matter even had a web bulb thermometer or digital psychrometer in their possession. The last technician said it was good enough to get around ten degrees of actual superheat no matter what.

    What is the truth?
    You are correct. Another correct answer is to use the manufacturer charging chart which usually requires a WB measurement. If you apply that formula to the manufacturer's charts, you will find that its dead on or less that 3° different than any target SH chart. That formula was derived by hvacrmedic, a pro member here.

    Keep looking for a tech. There are good ones out there.

    What field are you in?

Page 1 of 5 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event