    Occasionally I am getting code 12 error on Bryant 355MAV042080 furnace controlled via Evolution Control.
    Unit seems to be working just fine. How serious the problem is?

    Thanks,
    Mark

  2. #2
    Join Date
    Jul 2001
    Posts
    3,112
    Post Likes
    What is a code 12?

  3. #3
    Join Date
    Dec 2001
    Location
    St Louis, MO
    Posts
    196
    Post Likes
    code 12 is not an error code. it signals blower on after power up w/ a call for heat. blower runs for 90 seconds, then goes back to heat cycle.

  4. #4
    Join Date
    Sep 2005
    Posts
    16
    Post Likes
    Thread Starter
    Do I need to do anything with it or just leave it alone? My blower runs continuously, would it cause it?

    Thanks,
    Mark

  5. #5
    Join Date
    Dec 2001
    Location
    St Louis, MO
    Posts
    196
    Post Likes
    soory may have gave you bad info. I believe code 12 0n that furnace is BLOWER CALIBRATION LOCKOUT—This fault indicates that blower motor speed calculated for low heat is
    either less than 250 RPM or greater than 1300 RPM on 2 successive attempts at calibration. Control will
    auto-reset in 3 hours.

    Best call for service.