trane voyager locking out
trane raucc60ee
hi anyone have an idea why this trane locking out. it trips almost everyday or sometimes once a week. by the time i get the call, all the safety controls already closed. anyone has any idea? please help
-
09-05-2011, 04:49 AM #2
Regular Guest
- Join Date
- Feb 2008
- Location
- St. louis Mo
- Posts
- 10
.10 amp fuses across the the safteys. Have you taken pressure readings? Coil is clean?
-
09-05-2011, 09:08 AM #3
Professional Member
- Join Date
- Jan 2007
- Location
- Pittsburgh
- Posts
- 181
I would start with basics.. Filters/belt/coils. What your pressures look like ? voltage/amps ? Is there corrosion on UCP board ?
-
09-05-2011, 12:21 PM #4
Circuit 1, circuit 2, Both???
Narrows the possibilities!I'm good at making things cold...You can ask my first two wives!
-
09-05-2011, 03:00 PM #5
Regular Guest
- Join Date
- Nov 2010
- Posts
- 10
@BKS60-only the 2nd circuit trips. after i reset the system, pressures, amps, superheat and subcool is good. i'm in the process of putting a tattle tale on all the safeties. belts and filters are brand new.
-
09-05-2011, 03:05 PM #6
Regular Guest
- Join Date
- Nov 2010
- Posts
- 10
@coolerguy, their is no ucp board on this system, only relays, and timer motors for circuit 1 and 2.
-
09-05-2011, 05:08 PM #7
Make its a lot less to consider. I would obviously stay on the 2ns circuit only. You may try checking all fans for contactors, shafts and amps. Also I would check the lockout relay. i have found that the relays are failing and also the pins on the subbases are not making good contact. The N/O contacts on the back of the compressor circuit breakers have also been known to fail intermittently.
Just a few starting points!I'm good at making things cold...You can ask my first two wives!
-
09-05-2011, 05:48 PM #8
Professional Member*
- Join Date
- Aug 2008
- Location
- Austin, TX
- Posts
- 28
is there any active alarms before you reset the unit?
-
09-05-2011, 06:38 PM #9
I believe that unit will just open the lockout relay. There is not a control display to monitor alarms.
I'm good at making things cold...You can ask my first two wives!
-
09-05-2011, 07:01 PM #10
New Guest
- Join Date
- Jun 2011
- Posts
- 1
Sounds like you need to start using some taddle tales to isolate your problem.
-
09-05-2011, 09:13 PM #11
Regular Guest
- Join Date
- Nov 2010
- Posts
- 10
@BKS60, yes i have bypass the n/o contacts for the breaker of that compressor. and i swap all the relays from the 1st circuit but it still trips. i will try to spin the shaft on each cond fan manually, i only took amps and was under the rated load.
-
09-06-2011, 01:14 AM #12
Regular Guest
- Join Date
- Aug 2011
- Location
- Los Angeles, CA
- Posts
- 34
Is there a freeze stat on the unit? I have had a few Tranes act this way.
-
09-06-2011, 06:48 PM #13
Go to the terminal board and make sure that every screw is tight. Every one. No wire on it? Tighten it anyway. Some of those are safety connections and jumper strips.
I had a problem unit a couple of years ago, and darned if I didn't find a screw backed out about 3/4 turn.
After that, no problem.[Avatar photo from a Florida training accident. Everyone walked away.]