Results 1 to 13 of 18
    Nov 2010
    Confused trane voyager locking out
    trane raucc60ee
    hi anyone have an idea why this trane locking out. it trips almost everyday or sometimes once a week. by the time i get the call, all the safety controls already closed. anyone has any idea? please help
    St. louis Mo
    .10 amp fuses across the the safteys. Have you taken pressure readings? Coil is clean?
    Pittsburgh
    I would start with basics.. Filters/belt/coils. What your pressures look like ? voltage/amps ? Is there corrosion on UCP board ?
    Dec 2009
    Southern US
    Circuit 1, circuit 2, Both???
    Narrows the possibilities!
    I'm good at making things cold...You can ask my first two wives!
    Nov 2010
    @BKS60-only the 2nd circuit trips. after i reset the system, pressures, amps, superheat and subcool is good. i'm in the process of putting a tattle tale on all the safeties. belts and filters are brand new.
    Nov 2010
    @coolerguy, their is no ucp board on this system, only relays, and timer motors for circuit 1 and 2.
    Dec 2009
    Southern US
    Quote Originally Posted by Brokanic View Post
    Make its a lot less to consider. I would obviously stay on the 2ns circuit only. You may try checking all fans for contactors, shafts and amps. Also I would check the lockout relay. i have found that the relays are failing and also the pins on the subbases are not making good contact. The N/O contacts on the back of the compressor circuit breakers have also been known to fail intermittently.
    Just a few starting points!
    Aug 2008
    Austin, TX
    is there any active alarms before you reset the unit?
    Dec 2009
    Southern US
    I believe that unit will just open the lockout relay. There is not a control display to monitor alarms.
    Jun 2011
    Sounds like you need to start using some taddle tales to isolate your problem.
    Nov 2010
    @BKS60, yes i have bypass the n/o contacts for the breaker of that compressor. and i swap all the relays from the 1st circuit but it still trips. i will try to spin the shaft on each cond fan manually, i only took amps and was under the rated load.
    Aug 2011
    Los Angeles, CA
    Is there a freeze stat on the unit? I have had a few Tranes act this way.
    Southeastern Pa
    Go to the terminal board and make sure that every screw is tight. Every one. No wire on it? Tighten it anyway. Some of those are safety connections and jumper strips.
    I had a problem unit a couple of years ago, and darned if I didn't find a screw backed out about 3/4 turn.
    After that, no problem.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
