    Confused HELP PLEASE,,,THANKS

    Hi everyone,,Can someone help me with this,,,,,,My vaccum pump is not the best so when I vaccum the evaporator side of the split system and did not have any nitrogen,,instead i used R22 to purge the system,,,I presurise with r22 vacumm for 10 minutes,,,I do this 3 times and the last time i vacumm for one hour,,Can you tell me am i doing a big sin to purge with r22 instead of Nitrogen,,,please tell me cause if it is a very bad practice i will not do again,,,,Thanks Jocelyn

  2. #2
    Join Date
    Jan 2008
    Posts
    2,904
    Post Likes
    Might want to check the EPA rules for this question. You do have an EPA card, right?
    But hey, a lot of folks don't think we need that pesky ozone layer anyway.
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler

  3. #3
    Join Date
    Jul 2004
    Location
    Charleston, SC
    Posts
    930
    Post Likes
    Nitrogen and a regulator are much cheaper than an EPA fine! While a fine is probably not a reality for a small offence, it is still the wrong way to handle refrigerant. Do you have an EPA certification to handle refrigerant? If so, go read the book again!

    Seriously though, nitrogen is cheaper than refrigerant, and legal too. While you are at it, buy a micron gauge also. How long you run the pump is irrelevant, measure the results.
    "Customer Service" is not a department, it's an attitude!
    ???

  4. #4
    Join Date
    Sep 2011
    Location
    Canada NB
    Posts
    32
    Post Likes
    Thread Starter

    Recover

    Hi 2old2rock,,,Yes i have my card and i do recover the R22,,,I am just wondering,,is it a bad practice for the equipment,,,Thanks 2old2rock ,,,Jocelyn

  5. #5
    Join Date
    Sep 2011
    Location
    Canada NB
    Posts
    32
    Post Likes
    Thread Starter
    Thanks cartercrew,,sure appreciate your answer,,,now you have convinced and help me,,I am just a rooky,,I will learn,,,I real appreciate you helping me,,Your help is worth a fortune to me,,Thanks and have a good day,,,Jocelyn from Canada

  6. #6
    Join Date
    Jun 2011
    Location
    Hammond,La.
    Posts
    1,181
    Post Likes
    I think you may be defeating the purpose of triple evacuation by purging with the r22 because now you have moisture in your recovery tank with your r22.
    If you are recovering the refrigerant you are spending way too much time and wear on your recovery machine anyway and would be better off just pulling to 500 microns or below until you can maintain a 500/700 micron level for a while with the valves closed. N2 is cheap and the bottle and regulator aren't expensive either and you can just vent the N2 into the air before you start the vacuum process again.
    "I am for doing good to the poor, but I differ in opinion of the means. I think the best way of doing good to the poor, is not making them easy in poverty, but leading or driving them out of it."
    Benjamin Franklin, 1766

  7. #7
    Join Date
    Mar 2009
    Location
    Triad - North Carolina
    Posts
    543
    Post Likes
    Hi everyone,,Can someone help me with this,,,,,,My vaccum pump is not the best so when I vaccum the evaporator side of the split system and did not have any nitrogen,,instead i used R22 to purge the system,,,I presurise with r22 vacumm for 10 minutes,,,I do this 3 times and the last time i vacumm for one hour,,Can you tell me am i doing a big sin to purge with r22 instead of Nitrogen,,,please tell me cause if it is a very bad practice i will not do again,,,,Thanks Jocelyn

    EPA says yes, It's a big sin.

  8. #8
    Join Date
    Jan 2007
    Location
    Vancouver Island, B.C.
    Posts
    2,844
    Post Likes
    Quote Originally Posted by Huang View Post
    Hi everyone,,Can someone help me with this,,,,,,My vaccum pump is not the best so when I vaccum the evaporator side of the split system and did not have any nitrogen,,instead i used R22 to purge the system,,,I presurise with r22 vacumm for 10 minutes,,,I do this 3 times and the last time i vacumm for one hour,,Can you tell me am i doing a big sin to purge with r22 instead of Nitrogen,,,please tell me cause if it is a very bad practice i will not do again,,,,Thanks Jocelyn
    Jocelyn,
    The Canadian ODS act forbids you from 'venting' any CFC/HCFC refrigerant to atmosphere......it's a $200,000.00 fine if you get caught. A decent vacuum pump is only $300-400. It's not an option....get one or you should not be in the industry.
    "The quality you deserve is not expensive---it's priceless"

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Yes. As Doug pointed out, it is a BIG no-no, whether in Canada or here in the states.

    Use a micron gauge AND a vacuum pump to dehydrate your system first.

    You might want to break down and get a tank of N and a regulator so when you need to purge a system, you can use nitrogen instead of R22!!!!
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #10
    Join Date
    Sep 2011
    Location
    Canada NB
    Posts
    32
    Post Likes
    Thread Starter
    Quote Originally Posted by Rcb2875 View Post
    I think you may be defeating the purpose of triple evacuation by purging with the r22 because now you have moisture in your recovery tank with your r22.
    If you are recovering the refrigerant you are spending way too much time and wear on your recovery machine anyway and would be better off just pulling to 500 microns or below until you can maintain a 500/700 micron level for a while with the valves closed. N2 is cheap and the bottle and regulator aren't expensive either and you can just vent the N2 into the air before you start the vacuum process again.
    Thanks George,,I am getting N2 tomorrow,,all you said makes sense,,this is my priority tomorrow,,Thanks Jocelyn and have a good day

  11. #11
    Join Date
    Jun 2011
    Location
    Hammond,La.
    Posts
    1,181
    Post Likes
    He stated that he does recover the refrigerant each time in post #4 so I can't see any environmental violation in purging with refrigerant.. Bringing a system to just above atmospheric pressure and recovering is not a violation. Venting into the atmosphere is a different story.
    "I am for doing good to the poor, but I differ in opinion of the means. I think the best way of doing good to the poor, is not making them easy in poverty, but leading or driving them out of it."
    Benjamin Franklin, 1766

  12. #12
    Join Date
    Jan 2007
    Location
    Vancouver Island, B.C.
    Posts
    2,844
    Post Likes
    Quote Originally Posted by Rcb2875 View Post
    He stated that he does recover the refrigerant each time in post #4 so I can't see any environmental violation in purging with refrigerant.. Bringing a system to just above atmospheric pressure and recovering is not a violation. Venting into the atmosphere is a different story.
    Using a CFC or HCFC in Canada for leak testing is illegal......you can pressurize with N2 and an HF to lower the quantity of HF in a larger system.....but no CFC or HCFCs allowed for leak testing.
    The only case where it is allowed is if it's the original HCFC that was used in the system and is now being used; ie released from the receiver, to the rest of the system....
    "The quality you deserve is not expensive---it's priceless"

  13. #13
    Join Date
    Jun 2011
    Location
    Hammond,La.
    Posts
    1,181
    Post Likes
    Quote Originally Posted by Doug Lockhart View Post
    Using a CFC or HCFC in Canada for leak testing is illegal......you can pressurize with N2 and an HF to lower the quantity of HF in a larger system.....but no CFC or HCFCs allowed for leak testing.
    The only case where it is allowed is if it's the original HCFC that was used in the system and is now being used; ie released from the receiver, to the rest of the system....
    He is just attempting to triple evacuate the system with R22 rather than N2, no mention of leak testing.
    "I am for doing good to the poor, but I differ in opinion of the means. I think the best way of doing good to the poor, is not making them easy in poverty, but leading or driving them out of it."
    Benjamin Franklin, 1766

  14. #14
    Join Date
    Jan 2007
    Location
    Vancouver Island, B.C.
    Posts
    2,844
    Post Likes
    Quote Originally Posted by Rcb2875 View Post
    He is just attempting to triple evacuate the system with R22 rather than N2, no mention of leak testing.
    I agree with you .... Only explaining in Canada the only time it's legal to put in an HCFC into a system then blow it back out intentionally through a vacuum pump.
    "The quality you deserve is not expensive---it's priceless"

  15. #15
    Join Date
    Mar 2009
    Location
    Triad - North Carolina
    Posts
    543
    Post Likes
    I missed the Canada part, OOOOPPSS!!!

  16. #16
    Join Date
    Jan 2007
    Location
    Vancouver Island, B.C.
    Posts
    2,844
    Post Likes
    Quote Originally Posted by Keith73 View Post
    I missed the Canada part, OOOOPPSS!!!
    Yah .... you remember the country that hands you guys your lunch every Olympics in Hockey.....that'd be us Canada...EH!!

    Say, listen, just to help bury the hatchet on that......in 3 years when the Olympics are in Russia and your flights are heading out over us to Russia, why don't you guys have your men's hockey team drop into Canada and we'll get a couple of shinny games with our girls team to help you bring your game up a bit....
    "The quality you deserve is not expensive---it's priceless"

  17. #17
    Join Date
    Mar 2009
    Location
    Triad - North Carolina
    Posts
    543
    Post Likes
    Quote Originally Posted by Doug Lockhart View Post
    Yah .... you remember the country that hands you guys your lunch every Olympics in Hockey.....that'd be us Canada...EH!!

    Say, listen, just to help bury the hatchet on that......in 3 years when the Olympics are in Russia and your flights are heading out over us to Russia, why don't you guys have your men's hockey team drop into Canada and we'll get a couple of shinny games with our girls team to help you bring your game up a bit....
    Ok, we let you guys win a couple of games so don't get all cocky and all.

  18. #18
    Join Date
    Jun 2011
    Location
    Hammond,La.
    Posts
    1,181
    Post Likes
    Since when was a bunch of grown men figure skating a real sport anyway..
    "I am for doing good to the poor, but I differ in opinion of the means. I think the best way of doing good to the poor, is not making them easy in poverty, but leading or driving them out of it."
    Benjamin Franklin, 1766

  19. #19
    Join Date
    Sep 2011
    Location
    Canada NB
    Posts
    32
    Post Likes
    Thread Starter

    Thanks

    Quote Originally Posted by Doug Lockhart View Post
    Using a CFC or HCFC in Canada for leak testing is illegal......you can pressurize with N2 and an HF to lower the quantity of HF in a larger system.....but no CFC or HCFCs allowed for leak testing.
    The only case where it is allowed is if it's the original HCFC that was used in the system and is now being used; ie released from the receiver, to the rest of the system....
    Yes now i know i was not doing things right,,,I am buying nitrogen from now on,,it is better to do things the right way

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •