york split question,subcool response
2ton 15 yr old york split HP; txv; accumulator
cooling look good but i decided to check my unit white the september heat was hot.
Out amb 95, humidity 40
press; 77, 225
saturation temp 105 (looking for 95 at least) (10 above amb though)
inside; TEET per feildpc good- 80 in 60 out
SubCool abt 0
I added 16 oz over 45 min time period and got very little reaction to subcool.
Both pressures came up a little each time i added but settled back to the org pressures and sat temp.
Dont have much exp with York but looks like the average system txv.
The question; is the system low based on temp and pressures.
coils are clean.
-
09-03-2011, 10:42 PM #2
Professional Member
- Join Date
- Dec 2010
- Posts
- 52
should have said liquid line temp and saturation temp abt the same. 105
-
09-03-2011, 11:22 PM #3
Professional Member
- Join Date
- Apr 2011
- Location
- Florida
- Posts
- 87
what are your sub cool and super heat numbers
Aire Force A/C and heating
Florida
since 1988
-
09-03-2011, 11:56 PM #4
Regular Guest
- Join Date
- Dec 2009
- Location
- Fort Worth, Texas
- Posts
- 142
to be honest, the only numbers that are needed for troubleshooting are sh and sc. these are the two numbers needed. if you have 0 subcooling it means you are low on charge but we need sh to verify and it may lead us to need other info.
-
09-04-2011, 03:35 AM #5
New Guest
- Join Date
- Sep 2011
- Location
- Alabama
- Posts
- 3
I assume you read the 105 F, and the Sat temp at 225 is 109.5 not 105 so you have subcooling of 4.5. The DT at the evap is 20 F very good. The 77 P at your evap seems a hair low with those numbers but could be ok. I would have thought it would be closer to 85 P meaning a temp of 50. I bet your superheat was high and when you added the refrg it droped. Is the CFM lower than 800? Sounds like it might be. Check your superheat you may need a little more refrig.