Results 1 to 13 of 15
Thread: scrolls running backwards
-
09-03-2011, 07:31 PM #1
Regular Guest
- Join Date
- Jun 2011
- Location
- Fredneck MD
- Posts
- 12
scrolls running backwards
Ok heres one that will stump you. Well it stummped me and my HVAC buddies anyways.
The lobby unit in our building has been running 24/7 for 3 years with no problems. Then one day out of no where we found the main breaker for the unit tripped. After a quick investigation we reset the breaker and the compressors sounded horrible. we assumed a mechanical failure, but threw guages on it anyways and found the pressures to be equal while the compressor was "running".
So heres where it gets interesting. The fan is rotating properly, however my boss decided to switch 2 of the 3 legs on the compressor to change its direction and what do you know, the compressor ran perfect!
Hopefully i gave you guys enough info. So what do you think, were stumped?
-
09-03-2011, 07:54 PM #2
Professional Member
- Join Date
- Jul 2010
- Location
- So-Cal
- Posts
- 536
Disgruntled employee?
Sabatoge?
-
09-03-2011, 08:14 PM #3
Regular Guest
- Join Date
- Jun 2011
- Location
- Fredneck MD
- Posts
- 12
-
09-03-2011, 08:35 PM #4
A scroll with a switched leg and running backwards WILL sound like a train wreck and won't develop a pressure diferential. The fan(s) are probably single phase motors and don't give a hoot.
If it ran for three years and suddenly something like that happened then somebody or something did a change up.
Have there been any recent Bigfoot sightings in your area lately? Those hairy sob's have known to fish without a license.The picture in my avatar is of the Houston Ship Channel and was taken from my backyard. I like to sit outside and slap mosquitos while watching countless supertankers, barges and cargo ships of every shape and size carry all sorts of deadly toxins to and fro. It's really beautiful at times.....just don't eat the three eyed fish....
¯`·.¸¸ .·´¯`· .¸>÷÷(((°>
`·.¸¸..· ´¯`·.¸ ¸.·´¯` ·.¸>÷÷(((°>
.·´¯`· .¸>÷÷(((°>
LMAOSHMSFOAIDMT
-
09-03-2011, 09:11 PM #5
Regular Guest
- Join Date
- Jun 2011
- Location
- Fredneck MD
- Posts
- 12
-
09-04-2011, 04:07 AM #6
New Guest
- Join Date
- Sep 2011
- Location
- Alabama
- Posts
- 3
I have seen it years ago when the power company replaced a blown pole mounted transformer. They paced the 3-phase wire back differently. The phase shift on the wire change made it run backwards. It is not uncommen. Sometimes when the power goes out it happens.
-
09-04-2011, 09:26 AM #7
Guest
- Join Date
- Apr 2005
- Location
- where the beer flows like wine
- Posts
- 2,871
I encountered the very same problem with a two stages Carrier RTU, one of the compressors ran backwards for five years or so, nobody notice it, I also thought the compressor was shot but after swapping leads it ran like a champ, amazing it survive after running backwards for so long.
-
09-04-2011, 09:40 AM #8
Had a Trane unit do the same thing, one day the compressor was running backwards for no apparent reason, switched the leads and away it went.
Had the same thing with a 3 phase 7.5 hp blower motor.I'm not tolerating Political Correctness anymore, from now on it's tell it like it is.
Veto Pro Pak - The best tool bag you'll ever own
-
09-12-2011, 07:58 AM #9
Professional Member*
- Join Date
- Oct 2002
- Posts
- 675
Back to back three phase motors running on single phase (bad contactor or breaker causing missing leg) will recreate the missing leg. Three phase motor would work on a single phase supply then
This is how one can use a three phase motor on single phase service.
Maybe?
-
09-12-2011, 05:37 PM #10
Guest
- Join Date
- Apr 2005
- Location
- where the beer flows like wine
- Posts
- 2,871
-
09-12-2011, 06:36 PM #11
Professional Member*
- Join Date
- Feb 2006
- Location
- Float'N Vally, MS
- Posts
- 1,608
The OP didn't state if it is 3 or single phase. Older single phase have been know to reverse after a "short" power blip. The is why they had a delay relay on them.
Life is too short, Behappy!
TFMM
-
09-12-2011, 11:48 PM #12
-
09-13-2011, 12:04 AM #13


Reply With Quote