Thread: air conditioning used to cool 15 degrees now only 4

  1. #1
    Join Date
    Sep 2011
    Posts
    5
    Post Likes

    air conditioning used to cool 15 degrees now only 4

    Suddenly a 1.5 year old carrier air conditioning unit at my house that used to rapidly cool the house 10-15 degrees is now only able to cool it 2-4 degrees.

    A serviceman came out and checked the freon and amperage and differential and some other stuff and said the unit is working perfectly. They measured the output at the nearest vent and it was 46 degrees on a 65 degree day.
    The air coming out seems cool but the house just will no longer cool down?

    Question 1. What could cause this if the unit seems to be working.
    Question 2. If the temp outside is 64 should my air conditioner be able to get the house to 54 or does it only lower it 10 degrees if it's 80 in the house down to 70.

    Any experts have any ideas. I've been reading up on air conditioning and nothing seems to make any sense.

    Thanks,

    Dan
    Homeowner

  2. #2
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    First, the coolest temp you should try to attain is a setpoint of about 69 in residential. There are some folks who want it cooler than that, and some equipment can indeed get you there, but 54 would be bordering on refrigeration.

    Second, ask yourself, when did you perceive this change? The beginning of the season? On hot days only? After you heard a noise form the system?

    My point is that if the parameters are in place, and there was no work performed, then a supply temp like 46 should be cooling your house.

    It may be time to get another opinion, since we generally can't rely on readings that we haven't taken ourselves.

    My gut is telling me there is more to the story. Not that you are deceptive, mind you, but that there may be other pieces to this puzzle.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  3. #3
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    How high was the humidity in the house at 54F?

    Never try to get the indoor temp that low, especially on a cool day.

    Try it again when the weather is hot With a 75 to 80F indoor temp & 50% indoor relative humidity. The temp drop should be around 18 to 20F depending on where & how you take the temp.

    How energy efficient your home duct system, etc., is determines how much temp drop it will get below the outside temp.

  4. #4
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    Maybe we don't understand your post. Do you actually keep your home at 54 degrees? Most AC units are not designed to operate at this low an inside temp. What part of the country do you live in?

  5. #5
    Join Date
    Dec 2010
    Location
    Chandler, az
    Posts
    30
    Post Likes
    Well, I think it's clear. Replace your refrigerator instead of using your air conditioner to keep your food cool and preserved.

  6. #6
    Join Date
    Sep 2011
    Posts
    5
    Post Likes
    Thread Starter

    clarifications.

    Thanks for the jokes and questions.

    Here are some clarifications. The day we were testing it was not hot so I was trying to see how much I could cool the house below the ambient temperature and how long it would take. It was 65 and I was hoping it would drop to 55.

    I could only get 4 degrees cooler than starting temp of 65 it went down a few degrees.
    On another day at 83 it went down to 79, but while doing so the outside temp also dropped a few degrees so it's hard to say if it's doing anything.

    It's certainly not 15-20 degrees although I thought that's what it used to do though. It used to cool the house down in a half hour about 10-15 degrees.
    Now it does about 4 even though it checks out fine.

    Dan

  7. #7
    Join Date
    May 2011
    Location
    Ripley, WV
    Posts
    1,607
    Post Likes
    Did the technician by chance share any of his readings with you or discuss his findings with you? it would be nice to know what he saw and then we might be able to spot a human error or oversight.

  8. #8
    Join Date
    Apr 2009
    Location
    San Diego
    Posts
    75
    Post Likes
    check your airflow. Check all registers for airflow and make sure your return is getting indoor air not attic air. Make sure you have a clean filter and all registers are open with air blowing out of them. Next make sure your outdoor condenser has hot air (warmer than ambient) coming off the top of it from the fan. If both of the previous steps are done and OK then call your service tech because the next steps require the tools and skills of an HVAC technician

  9. #9
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Quote Originally Posted by C Combs View Post
    check your airflow. Check all registers for airflow and make sure your return is getting indoor air not attic air. Make sure you have a clean filter and all registers are open with air blowing out of them.

    Next make sure your outdoor condenser has hot air (warmer than ambient) coming off the top of it from the fan. If both of the previous steps are done and OK then call your service tech because the next steps require the tools and skills of an HVAC technician
    Good advice.

    Also, buy a humidity gauge at a hardware store.
    When it is 78F & 50% or higher humidity in your home, a 10 or 12-SEER condenser will normally have an 18 to 20F air temp rise off it.

    It appears the indoor coil is not absorbing an adequate heatload.
    The condenser test will provide a clue concerning how much heat is being discharged to the outdoors.

    You will need to find a competent Tech to verify & fix any problems.

  10. #10
    Join Date
    Sep 2011
    Posts
    5
    Post Likes
    Thread Starter

    ambient air and fan

    I think that the fan on the unit is blowing out ambient temperature air, not hot air. It feels almost the same. I'm going to get a gauge and measure it and I'll report back.

    Is it possible for the unit to check out fine in terms of typical measurements that a typical technician would make and still have a problem?


    Thanks for all the input,

    Dan

  11. #11
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by whimser View Post
    I think that the fan on the unit is blowing out ambient temperature air, not hot air. It feels almost the same. I'm going to get a gauge and measure it and I'll report back.

    Is it possible for the unit to check out fine in terms of typical measurements that a typical technician would make and still have a problem?


    Thanks for all the input,

    Dan
    1) There is no "typical" tech. However, you want a competent tech. It may be an opportunity for a second opinion.

    2) Without heat load, you can't test the system properly. No system would respond in the manner you expected under those conditions.

    What were the conditions on the day you decided to call out a contractor?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  12. #12
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes
    If you know that the Temperature Difference changed from 15 to 4,
    you KNOW
    the unit is Very Ill.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  13. #13
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by dan sw fl View Post
    If you know that the Temperature Difference changed from 15 to 4,
    you KNOW
    the unit is Very Ill.

    I don't think that's what he said.

    He said it used to cool 15 decrees on a day where cooling was required.

    They he said he tested it on a day with no heat load and got 4 degrees.

    Not the same thing.

    I think most of us can imagine what happened on the day without heat load as he ran the unit continuously......
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  14. #14
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes

    Hmm # 6 by OP

    Quote Originally Posted by timebuilder View Post
    I don't think that's what he said.

    He said it used to cool 15 decrees on a day where cooling was required.

    They he said he tested it on a day with no heat load and got 4 degrees.

    Not the same thing.

    I think most of us can imagine what happened on the day without heat load as he ran the unit continuously......
    Post # 6

    " ...
    I could only get 4 degrees cooler than starting temp of 65 it went down a few degrees.
    On another day at 83 it went down to 79, but while doing so the outside temp also dropped a few degrees so it's hard to say if it's doing anything. "

    With 83'F inside, the diffusers ( vents) should provide air at about 61- 65'F.
    I guess clarification is not clear.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  15. #15
    Join Date
    Dec 2006
    Posts
    82
    Post Likes
    years ago the same thing happened to me... then I flushed out my condenser coil. Could it be that simple?

  16. #16
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by dan sw fl View Post
    Post # 6

    " ...
    I could only get 4 degrees cooler than starting temp of 65 it went down a few degrees.
    On another day at 83 it went down to 79, but while doing so the outside temp also dropped a few degrees so it's hard to say if it's doing anything. "

    With 83'F inside, the diffusers ( vents) should provide air at about 61- 65'F.
    I guess clarification is not clear.
    No, it isn't.

    We have no idea how long the system was permitted to run before that reading was taken, do we? What else was going on? What kind of other variables are in play that could have kept the heat load from the evaporator?

    Nope. Clear it is not.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  17. #17
    Join Date
    Nov 2008
    Location
    Chapel Hill, NC
    Posts
    1,070
    Post Likes
    Quote Originally Posted by whimser View Post
    Is it possible for the unit to check out fine in terms of typical measurements that a typical technician would make and still have a problem?
    Not if the tech knows what he's doing. Your first post said "They measured the output at the nearest vent and it was 46 degrees on a 65 degree day". 65 degrees inside the house, or 65 degrees outside? If the former, that's a 19 degree differential which is good (if you don't have a plugged filter). You now say it's blowing ambient temp air - ie differential of zero. Which is it?

  18. #18
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by timebuilder View Post

    I think most of us can imagine what happened on the day without heat load as he ran the unit continuously......
    I don't think it is a problem to tell him. If you try to run an AC unit too cold, the coil temperature drops below freezing. Then the coil starts to build ice fairly rapidly. This tends to be very bad for compressors. It is also why AC equipment cannot maintain temperatures much below 70 degrees F.

    Quote Originally Posted by kwilcox View Post
    years ago the same thing happened to me... then I flushed out my condenser coil. Could it be that simple?
    A competent technician would see this in an analysis of the system.



  19. #19
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    I one heard about a guy who was told his coil was frozen, so he decided to clear the ice himself when the tech left.

    With an ice pick.

    I'd rather the guy called that "competent" tech, perhaps from another company.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  20. #20
    Join Date
    Dec 2006
    Location
    toronto, canada
    Posts
    605
    Post Likes
    Quote Originally Posted by whimser View Post
    It's certainly not 15-20 degrees although I thought that's what it used to do though. It used to cool the house down in a half hour about 10-15 degrees.
    Now it does about 4 even though it checks out fine.
    I really doubt this, the reason why the OP thought the ac was wrong.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •