True Reachin Cooler Issue
Hello people,
Been at this for over 30 years but I have a reach in cooler thats driving me nuts. Tssu72 (true) compressor overheating. Replaced compressor and cap tube. Blew out condenser & evap. Unit still running with high head..... almost 300 psi back pressure 20 psi............ 134a refrigerant. any help would be appreciated
Thanks
Frank
-
09-03-2011, 11:51 AM #2
This is just the welcome area. If you click the red triangle in the top right of your post, a moderator will move it to the refrigeration forum.
-
09-03-2011, 11:53 AM #3
Regular Guest
- Join Date
- Sep 2011
- Posts
- 9
Stupid newbee here
Thank you
-
09-03-2011, 11:55 AM #4
-
09-03-2011, 12:03 PM #5
Thread moved by OP request.
09-03-2011, 12:05 PM #6
Regular Guest
- Join Date
- Sep 2011
- Posts
- 9
thanks for your help
09-03-2011, 09:27 PM #7
Professional Member
- Join Date
- Sep 2008
- Location
- Cedar Rapids, IA
- Posts
- 473
Sounds like you have an obstructed cap tube. Could be a piece of debris got into it either before or after you installed it. Might be wrong size or too long as well. When the parts boys pick it out of a bin they sometimes grab the wrong one. I've had parts labeled in the bag correctly but obviously the wrong part.
12-31-2011, 09:31 AM #8
Professional Member
- Join Date
- Dec 2011
- Location
- USA
- Posts
- 66
I would suspect the cap tube sizing or the amount of charge, because if it is 30 years old it would not have been manufactured with 134a.