09-19-2011, 05:10 PM #14
For anyone still interested, replaced the motors with OEM and that has fixed my problem. Thanks everyone for all of your inputs!!
-
09-19-2011, 10:10 PM #15
Professional Member
- Join Date
- Jan 2003
- Location
- Kansas City
- Posts
- 1,476
I'll bet they draw slightly over fla stamped on the side of the motor. Most of the Aaon condenser fan motors I see run well into the service factor.
-
09-20-2011, 09:19 AM #16
Yea, they did! FLA was 2.0 however i was pulling 2.2. I noticed the motor was also considerably larger (depth) than the A/M's. I figured it must be more run windings. Also, I noticed it was open-type motor (ahu motor) but with a rain guard that doubles as a ventilator for the motor windings. (Fixed Centrifugal fan blades)
What a bunch of BS!!
It's hard to stop a Trane - Until you apply line voltage to it!!