    For anyone still interested, replaced the motors with OEM and that has fixed my problem. Thanks everyone for all of your inputs!!

  2. #15
    Join Date
    Jan 2003
    Location
    Kansas City
    Posts
    1,478
    I'll bet they draw slightly over fla stamped on the side of the motor. Most of the Aaon condenser fan motors I see run well into the service factor.

  3. #16
    Join Date
    May 2011
    Location
    Fort Worth, Texas
    Posts
    49
    Yea, they did! FLA was 2.0 however i was pulling 2.2. I noticed the motor was also considerably larger (depth) than the A/M's. I figured it must be more run windings. Also, I noticed it was open-type motor (ahu motor) but with a rain guard that doubles as a ventilator for the motor windings. (Fixed Centrifugal fan blades)

    What a bunch of BS!!


    It's hard to stop a Trane - Until you apply line voltage to it!!