Yep..
Add some gas and you will settle down.
Probably even bring your suction pressure down, too.
Bonus points for the OP if he can explain why suction will drop...
09-02-2011, 04:48 PM #15
09-02-2011, 04:49 PM #16
- Jul 2010
- 53
sorry for the confusion.. yes that is correct, I have about 12F of superheat and a couple degrees of subcooling, at best.. I had to run to grab some parts for another job, but will re-measure in a little while... as for now, I didn't want to add gas just yet.. wanted to be sure
09-02-2011, 04:50 PM #17
- Jul 2010
- 53
I keep mixing my lines up, and it came out in the form of subcooling/superheat confusion... yes, I have about 12F of superheat coming into the compressor via the suction line... the liquid line has nearly no subcooling to it.. I am going to re-attach the gauges in a bit, when I return to the site, to be sure of my numbers I quoted above.
09-02-2011, 04:51 PM #18
- Jun 2003
- Gulf Coast
- 145
09-02-2011, 04:54 PM #19
- Jul 2010
- 53
this was from the manufacturer's information... suction pressure will drop on the suction side when you add refrigerant since you have more refrigerant to absorb heat... since there is more refrigerant you will have more refrigerant to absorb the energy and will result in less liquid refrigerant turning into a gas, or vaporizing
what do I get?
09-02-2011, 04:56 PM #20
09-02-2011, 04:58 PM #21
- Jul 2010
- 53
how so? It has to do with the heat absorbed by the refrigerant and the vapor pressure of the refrigerant coming back to the compressor... Guess I am a little lost as to what you are looking for here for an answer
09-02-2011, 05:01 PM #22
- Jun 2003
- Gulf Coast
- 145
Did I miss the Model Number if not I think we need it
09-02-2011, 05:04 PM #23
09-02-2011, 05:06 PM #24
- Jul 2010
- 53
Greater subcooling
09-02-2011, 05:07 PM #25
09-02-2011, 05:08 PM #26
- Jul 2010
- 53