Thread: no superheat, no subcooling
-
09-02-2011, 03:15 PM #1
Professional Member
- Join Date
- Jul 2010
- Posts
- 53
no superheat, no subcooling
Here is the situation... Design pressures are 150/300psi with 12 degree subcooling...
Actual conditions are 92Psi liquid at a temperature of 69F. High pressure side is at around 220Psi and about 12F BELOW saturation temperature. Cooling isn't really doing much indoors and runs constantly.
Is the compressor on the way out or is there a charge issue here. Forgive me as I am fairly new to the service industry.
Thanks in advance guys
-
09-02-2011, 03:27 PM #2
Professional Member
- Join Date
- May 2009
- Posts
- 247
you have 14 deg superheat on r22 at that pressure and temp. The 92 is the suction not the liquid. The liquid (or high pressure or head pressure) temp should read below the saturation temp (it does SUBCOOL the refrigerant after all).
Your suction pressure is kinda high. This could be caused by hot temperature inside or high airflow. Is this a txv system?
-
09-02-2011, 03:27 PM #3
Professional Member
- Join Date
- Jul 2010
- Posts
- 53
R22 is the refrigerant
-
09-02-2011, 03:29 PM #4
I am kind of lost in your post...
Fill this out for me:
Refrigerant type (22,410,134)?
Type of system (split, package, chiller)?
Metering device (TXV, orifice, cap tube)?
Suction pressure?
Suction line temp?
Liquid line pressure?
Liquid line temp?
Return air temp?
Temp drop across the evap coil?
This will help us get started.UA LU189
10mm, because it's better than .45acp
-
09-02-2011, 03:47 PM #5
Professional Member
- Join Date
- Jul 2010
- Posts
- 53
I'll get to a laptop quick and fill that out..
-
09-02-2011, 04:03 PM #6
Professional Member
- Join Date
- May 2009
- Posts
- 247
What is your coil temp difference? Do you have duct leakage to have high suction like that?
-
09-02-2011, 04:05 PM #7
Professional Member
- Join Date
- Jul 2010
- Posts
- 53
-
09-02-2011, 04:17 PM #8
no that means you have 12* superheat. Line temp - Sat temp = superheat for suction and subcool for liquid.
I really reccomend you learn what this is, the superheat / subcool as you can not diagnose a refrigeration issue w/o this. It's kinda like your blood pressureIt's hard to stop a Trane. but I have made one helluva living keeping them going.
-
09-02-2011, 04:18 PM #9
You have 14*F superheat
You have 0*F subcooling
That 0*F subcooling tells me you are way undercharged.UA LU189
10mm, because it's better than .45acp
-
09-02-2011, 04:22 PM #10
-
09-02-2011, 04:27 PM #11
Something
is not adding up here. How can you have 12-14 degree superheat and no subcooling? The TXV will be wide open with no liquid to it, only vapor. S/H should be much higher.
-
09-02-2011, 04:34 PM #12
-
09-02-2011, 04:37 PM #13
02, have you tried adding gas? I would start by adding until you see you liquid line temp start to drop a bit. No more than 2-3lbs though.
If you don't have the manufactures recommendation on target subcooling I would shoot for 10*F to start. Check your temp drop and superheat and report back to us.UA LU189