help me understand guts of outdoor unit
I have a nearly-new Bryant heat pump (213BNA030-A ourdoor unit) installed at my house... works great so I'm not asking for fix-it help!
I'm an engineer and I've been reading this site and just want to see if I understand what all these parts are in the outdoor unit.

Can you tell me if I have this right?
1- horizontal brass thing -- reversing valve (with orange wires leading to solenoid to actuate it)
2- pink wires -- to thermistor for determining when to defrost?
3- There seems to be 2 pressure switches -- one with blue wires (right on output of compressor) and one with yellow (right before liquid line exits unit) Why 2?
4- The pipe with the label "336530701" on it -- is that the piston metering device for when running in heat mode? (indoor coil has TXV)
5- black cylinder at bottom of pic (between reversing valve and compressor high-side I think). What is it? It looks like some sort of mini-accumulator but is much smaller than the thing I *know* is the accumulator on the top right of the pic.
Thanks!
-
09-01-2011, 04:05 PM #2
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
09-01-2011, 04:18 PM #3
Professional Member*
- Join Date
- May 2011
- Location
- Ripley, WV
- Posts
- 816
#1 yes thats the reversing valve
#2 The pink wires go to the defrost switch/thermostat. (no thermistors on this make/model.)
#3 There are two different switches one is a low pressure switch the other a high pressure.
#4 Header leading into the outdoor coil.
#5 As stated by previous poster that is the discharge muffler.
-
09-01-2011, 04:21 PM #4
Regular Guest
- Join Date
- Jun 2011
- Location
- Oregon
- Posts
- 11
Thanks so far... So is there no metering device on the outdoor unit? Indoor is a cased coil CNPHP3617 which says it has a TXV. What does the metering when in heat mode, the TXV on the inside coil still?
-
09-01-2011, 04:34 PM #5
To help identify components, you'll find a copy of the electrical schematic on the back of the service panel cover. You can also do a google search and find a copy of the installation manual and data sheets using part of the model number.
-
09-01-2011, 04:35 PM #6
Professional Member*
- Join Date
- May 2011
- Location
- Ripley, WV
- Posts
- 816
If you look at the lines going into the outside unit you will see a small line and a bigger one. The smaller one brazes in just like the big one, but notice there is a nut at the end of the smaller line? Inside that area there is whats called a piston orifice, in cooling mode it moves very slightly in one direction and allows unrestricted refrigerant flow around it to your indoor TXV, in heating mode it goes the other direction and seats inside its holder and only allows refrigerant to flow through a hole in the center of it and that causes the pressure drop needed to operate in heat mode. I hope the Mods don't kill me for giving that much info.
-
09-01-2011, 04:41 PM #7
-
09-01-2011, 04:45 PM #8
Professional Member*
- Join Date
- May 2011
- Location
- Ripley, WV
- Posts
- 816
-
09-01-2011, 05:05 PM #9
Regular Guest
- Join Date
- Jun 2011
- Location
- Oregon
- Posts
- 11
Aha, got it. Having read about a piston on this site over and over I just always imagined it to be bigger and easier to spot (like a TXV is pretty easy to find!) Makes sense, so it's in here right where the liquid line connects to the outdoor unit.

Thanks for the details, I promise I'm not ripping this thing apart, just like to know how things work. Wish I'd studied more before buying it, but hey, it works.
Is there some justification for using a TXV on the indoor coil and yet a piston on the outdoor on this heat pump? Obviously this is a lower-end 13 SEER setup and it's cheaper to only have 1 TXV, but how do they decide on which side to use which device? I'm in Oregon, this will probably be running in heating mode 90% of the time and cooling in 10%, and yet I have the fancy txv only in cooling...
-
09-01-2011, 07:41 PM #10
With the reliability of TXVs these days, be glad you only have 1!!!
My Tappan is 14 SEER with variable speed and it is the same way, TXV in and piston out. Has an accumulator to protect the compressor. I'd rather have it that way than TXV and no accumulator.
-
09-01-2011, 07:54 PM #11
This is what happens when manufacturers have to please the government.
For example, the NEC (national electrical code) preamble reads (90.1 B)
"...Compliance therewith and proper maintenance results in an installation that is essentially free from hazard but not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use."
This means that when a bureaucracy decides on a standard, it is the meeting of the standard ITSELF that is the point of interest, rather than the actual sensible construction or end result operation of the equipment.[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:


Reply With Quote