Trane Intellipak
What would cause an Intellipak to stay at Unit Stopped,if Bms input to unit start point are made. If I press auto it goes back to unit stopped, resetting the unit will usually start it. There are no alarms displayed.
-
09-01-2011, 03:07 PM #2
Regular Guest
- Join Date
- Aug 2011
- Location
- Los Angeles, CA
- Posts
- 34
Is there any thing else in the unit that will cause an 'externalanswer stop' I.e. duct detector or occupancy switch.
-
09-01-2011, 03:59 PM #3
Professional Member
- Join Date
- May 2002
- Location
- Long Beach, New York
- Posts
- 83
No only thing they control is stop start, no duct detectors.
-
09-01-2011, 04:53 PM #4
Regular Guest
- Join Date
- Aug 2011
- Location
- Los Angeles, CA
- Posts
- 34
Can you run it in service test?
-
09-01-2011, 05:16 PM #5
Professional Member
- Join Date
- Mar 2010
- Location
- Hot Desert SW
- Posts
- 27
Could be completely unrelated to your problem but....
I ran into this exact issue on a tridium based system/ Intellipak, and turns out mechanical contractor had replaced a VAV box on the job and never called us out to commission the VAV in Tridium. The Intellipak and VAV both had the same Node ID. Commissioned the VAV box and problem never happened again
-
09-01-2011, 05:38 PM #6
-
09-01-2011, 08:13 PM #7
Regular Guest
- Join Date
- Jun 2006
- Location
- Midwest
- Posts
- 284
I have seen this a few times on Intellipaks with an LCI-I/Lon board being used for comm. If unit has LCI-I, Switch unit control mode from BAS to LOCAL and see if unit starts.
-
09-01-2011, 08:44 PM #8
Professional Member
- Join Date
- May 2002
- Location
- Long Beach, New York
- Posts
- 83
Thanks for the replys. We only start stop unit through TB4 board, which I tried jumping out just to be sure. It was as if the stop button had been pushed but I know no one did and pushing auto would have started it. Any chance the RTM board is bad?
-
09-12-2011, 08:43 PM #9
Professional Member
- Join Date
- Aug 2010
- Location
- Middle GA
- Posts
- 91
I have seen the ribbon cable behind the keypad going to the circuit board on the HI become delaminated. This will cause difficulties in going from stop to auto and vice versa. I have temporarily fixed it by putting a paper clip on the ribbon cable to hold it together.