Hey guys,
I have read several of the threads concerning Carlyle unloaders but I am still not sure of what my problem may be. I have a Carlyle 06D compressor, 6 cylinder with two pressure controlled unloaders. R22 with 200 psig head and 100 psig suction. The unit starts off at these pressures. I have a feeling that both unloaders may be the problem but everything I have read seems to indicate that they should not unload unless suction pressure is low. Also, at least one of them is leaking at the control setpoint adjustment nut. If the diaphram is leaking wouldn't this cause the unloader to stay in the unloaded position? Is it sensible that both unloaders has failed? I did not do a pump down test to see if my valves are leaking by. Oh yeah, my space temp is 76* and OAT was 85* so I should definitely have enough load. How do I determine whether I am looking at an unloader problem or a valve problem?
-
09-01-2011, 12:41 AM #2
start by attempting to pump down the compressor
RTFM!!!
-
09-01-2011, 07:16 AM #3
Regular Guest
- Join Date
- Jun 2010
- Location
- West Kentucky
- Posts
- 18
I guessed that might be my reply. I just didntThink of it at the time. I got hung up on those unloaders thinking they may be the problem, I couldnt see the forest for the trees.
-
09-09-2011, 10:36 PM #4
Regular Guest
- Join Date
- Feb 2011
- Location
- colorado mountians
- Posts
- 117
Shut down the suction king valve slowly and watch an amp probe to check/ set those unloaders along with the suction gage
-
09-10-2011, 05:57 AM #5
Professional Member
- Join Date
- Apr 2006
- Location
- mechanical room
- Posts
- 1,212
well the first thing i would do is find the rla on the compressor, and compare it to your actual amps
-
09-10-2011, 11:14 AM #6
Professional Member
- Join Date
- Apr 2007
- Location
- Pa
- Posts
- 738
Check valves. Did you check heads to see if one is hotter than the other?
-
09-11-2011, 11:06 AM #7
Professional Member
- Join Date
- Jul 2007
- Location
- New Jersey
- Posts
- 3,031


Reply With Quote