Thread: 10 ton goodman ac
-
08-31-2011, 07:05 PM #1
New Guest
- Join Date
- Aug 2011
- Posts
- 4
10 ton goodman ac
Having trouble with an ac unit, need help!!
-
08-31-2011, 07:06 PM #2
Regular Guest
- Join Date
- Jan 2011
- Location
- TN
- Posts
- 93
more info
-
08-31-2011, 07:09 PM #3
New Guest
- Join Date
- Aug 2011
- Posts
- 4
Head pressure does not move off of 150, comp runs for bout a min, suction drops to 50, internal overload takes it out
-
08-31-2011, 07:21 PM #4
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,254
this thing got a model #
you sure the hoses are working?
does this thing have service valves?
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
08-31-2011, 07:25 PM #5
New Guest
- Join Date
- Aug 2011
- Posts
- 4
model ckl-120-3l
brand new set of hoses and manifold
it does have valves, thats how i read the pressures
-
08-31-2011, 08:50 PM #6
sure its OL and not low pressure switch?
-
08-31-2011, 09:05 PM #7
Amp draw?
-
08-31-2011, 10:10 PM #8
internal overload is usually caused by compressor getting too hot and that takes longer than 1 minute. Your low pressure switch will cause unit to shutdown as you explained. Quick way to check that is check for 24 volts across the low pressure switch. It will be 0 if all is good. It will be 24V it the low pressure switch opens. of course you will see 0 until the unit shuts down and the contactor plunger pops out then at the exact same time you will see 24 V at your meter.
-
09-01-2011, 08:03 AM #9
New Guest
- Join Date
- Aug 2011
- Posts
- 4
Contractor stays in and the fan stays running, company terminals shows open, its a fixed orifice system, could the problem be there?